• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Recent content by Daltondbl

  1. D

    DRASH Unit AC issue

    Thank you! This thing has been a booger with a few things. But I’ve got it all sorted except for this. I talked to someone that said timers were a big issue on them and the “cool” switch runs through timers and relays to open and close the hot gas valve and maybe that was closing and making the...
  2. D

    DRASH Unit AC issue

    This is it. 35KW generator, 8 ton AC. I think these were set at 16% initial torque at 10 second ramp time (if that’s right). Once the refrigerant equalizes the soft starter will start it and the compressor will pump but the compressor will overload after about 5 seconds of running and stop...
  3. D

    DRASH Unit AC issue

    Contractor has 24v to it and once the 24v has run through all the safeties and switches it completes the circuit and closes the soft starter. I’ve been told that timers are an issue on these as well. And that it could be something between the hot gas valve and the “cool” switch causing the...
  4. D

    DRASH Unit AC issue

    Yes, on these, in order for the soft starter to actually engage with the 24v. The 24v has to flow through all of the safeties in order for it to pull in and I have traced where the 24v comes out of the last switch and I have 24v which then runs into a timer and a relay which then tells the soft...
  5. D

    DRASH Unit AC issue

    I have the schematic for it, the 24v runs through all the pressure switches and given all you those safeties are closed, the 24v goes to a relay and then into the contactor. The starter pulls in like it’s supposed to and stays pulled in but the compressor is tripping out on something. Unless I...
  6. D

    DRASH Unit AC issue

    Maybe this is in the right location but anyway. I have a 2008 DRASH unit, generator works perfectly but my issue lies with AC unit itself. Specifically getting the AC compressor to start and pump. If the soft starter starts the compressor, you can hear it run but it will not pump the...
  7. D

    M200a1 MICLIC

    I really just bought it for shows to display for when the trailer is complete, or somewhat complete
  8. D

    M200a1 MICLIC

    I do not. I’ve ordered a paperback but it hasn’t got here yet. Thanks!
  9. D

    M200a1 MICLIC

    Anyone have the part number on the hydraulic cylinder that raises the launcher assembly ?
Top