Converting a 005A with a Digital Controller
Guyfang
26,119
Burgkunstadt, Germany
That was in 1977. My Mentor was a French guy who had to leave France in a hurry in 1961 due to the attempt to over through Charles De Gaulle. He was a SP/5. He was teaching me to be more "Electrified", as he put it. He almost died that night. Not because of the fire, smoke or general mayhem. No. Laughter almost undid him. Gil just passed away a few months ago. I bet he is still laughing in Heaven.
peapvp
1,417
Basehor, KS
Today is the day.
Larry's @Cowhunter 005A is running now with the DC 70 MeBay and everything works as intended
The wiring diagram is attached to this post as pdf
The only issue we ran into is the new coolant temp transducer. The MeBay cannot handle any resistance larger then 999 Ohm in their Sensor tables when defining the sensor for correct display.
We found a alternate Transducer from Amphenol WT083B001 from Mouser for around 9 bucks, which has the temperature / resistance curve the Mebay can handle.
We will post a update once the new sensor is installed and the MeBay Coolant Temp Sensor Curve has been updated
Note:
Please proceed at your own risk. Support and trouble shooting from our end is pretty much limited due to time constraints.
Scoobyshep
2,021
Florida
Today is the day.
Note:
I am glad you posted about the temp sender i was having the same issue and hadnt dug deeper into it yet.
peapvp
1,417
Basehor, KS
A few after thoughts on this project.
Normally we use only Made in USA products for obvious reasons. This was our first time branching out into uncharted territory when it comes to the origin of the MeBay Controller.
The MeBay Controller is a Domestic Chinese Product and when compared to other Domestic Chinese Controllers, it ranks in the upper price category in the Chinese Market. It is on average 50% more expensive then domestic Chinese low end controller.
As far as we can tell, the MeBay Controllers are available via eBay / Amazon in the USA only and are shipped via Postal Mail from China direct after purchase. We have not found a US Seller who has US stock of any of those controllers. At least at the time Larry ordered his DC 70 on Amazon in November 2024.
The available manuals for the Controller it self and the PC based Software to configure the Controller, are at times confusing, as the translations were apparently done by a translator whose English is his/her second language. It may have been translated by Google Translate etc.
The only software related issue I could find until this point, is the maximum Ohm Value for the Coolant Temperature Sensor which can be entered into the Parameter Software on the PC / Labtop.
The manual states a maximum of 9999 Ohm, but the software will allow only values to be entered up to 999 Ohm.
The manual also states that the outputs are Relay Dry Contacts with a maximum rating indicated in their wiring diagram.
If you find conflicting values for maximum current / voltage, use the lowest value you find.
It is also imperative that the DC 70 is supplied 24 VDC Power at all times, especially when the Genset is running and the E-Stop function is used to shut down the running Genset. As per MeBay manual, damage to controller may occur if the Controller looses power during a shut down.
Our Wiring diagram reflects that note in the Manual.
It is further vital to use a sufficient number of Suppression Diodes ( We used 1N5408 ) for all inductive devices, as the manual states here as well, that the lack of those suppressors could cause damage to the Controller.
Looking at the retail online pricing of around ~ US$ 225.00, it becomes clear that these devices use domestically produced semi conductors and passive components which are better then average for the Chinese Domestic Market, but are sub standard compared to parts made offshore by US Manufacturer.
The QA is more lenient in China and allows for lower pricing as they have less rejects in the QA process, which in turn then lowers the overall quality of the end product.
Please keep this in mind when deciding on retrofitting your genset.
We will update this Thread if more or important issues arise.
Scoobyshep
2,021
Florida
Today is the day.
Note:
I ordered one from china took 2 months with no shipping data. somewhere around month 1 I went through amazon and it took 2 weeks. now i have a spare.
peapvp
1,417
Basehor, KS
Update:
First things first. I updated the wiring diagram to REV 1.2
Corrections and additions in REV 1.2:
1. The PIN Labels for Low Fuel Level Switch FL-1 were corrected to C and D
2. We added the three color dots on the CR27 Half Bridge Rectifier in the drawing on CR27
We attached the latest Manual for the MeBay DC70D MK2 and DC70DR MK2 ( R indicates that it has built in RS 485 )
Larry ( @Cowhunter ) ran the Generator today for 30 minutes with 15 KW Load with no problems
We still have two things left do to:
Adjusting the CT Ratio from MeBay default 500/5 to show correct Amps / KW on display ( showing 2/3 of actual AMP / KW )
Parameter: Group 1) Basic Settings Parameter: #3 CT Rate
or
change the MeBay Controller from currently selected 3 Phase 4 Wire Mode to 2 Phase 3 Wire Mode ( Wiring Diagram Page 15 Bottom)
Parameter: Group 1) Basic Settings Parameter: #2 Gens AC System
In the next few days I will post the configuration for the Inputs for Coolant Temp Switch, Oil Pressure Switch and Low Fuel Level Switch as they can be selected as Normally Open or Normally Closed
peapvp
1,417
Basehor, KS
Update:
Larry ( @Cowhunter ) and myself tied the last three missing items together.
First we uploaded the temperature / resistance for the new but not yet installed Amphenol Coolant Temp Sensor from Laptop to DC70DR MKII
Next we did the automatic flywheel teeth calculation
for this generator has to be able to produce power so MeBay can sense the Frequency and the rated rpm has to be set to 1800 rpm
Then the crank disconnect has to be set to #4 RPM / Hz
then, while Genset is running, press down key and start key for about one to two seconds
MeBay will display this screen for two seconds after successfully calculating flywheel teeth
Note: the bottom screen indicator will briefly show Alarming in red while calculating and displaying teeth count
this number will be automatically saved to engine parameter “flywheel teeth”
the mpu Larry installed is now activated and starts showing rpm starting at around 150 rpm when engine is cranked
Last item was the adjustment of the current transfer ratio
Larry connected his current clamp to all three phases and we compared those to what MeBay indicated on Gen Screen with CTR set to MeBay default 500/5
the correction needed was 1.36
500 x 1.36 =680
we entered 680 for ctr and now that is working as well
Note:
We used the existing Current Transformer with the multi turn wires going through it
we will post a separate update on the Amphenol Coolant Temp Sensor in the next few days
peapvp
1,417
Basehor, KS
Update #1
the Amphenol WT083B001 coolant temp sensor seems to be working with the MeBay and the table we uploaded yesterday. However Larry ( @Cowhunter ) had to stop getting Genset to full operating temperature since today is Mother’s Day.
There is app difference of 10F between actual temperature and indicated temp on MeBay which I think is good enough for all purposes
The more important issue is the fact that data sheet table for temp vs resistance did not match the sensor Larry received from mouser.
This is a low cost temp sensor the automotive manufacturers use in electric vehicles to monitor coolant which circulates and cools the batteries during charging primarily
Larry had to create his own table
temperature in F and resistance in kilo ohm
Larry heated a pot of water up to boiling and then took readings on the way down while pot of water was cooling
to install the sensor Larry used a fitting and jb welded the sensor into the fitting and we let it cure for 72 hours
peapvp
1,417
Basehor, KS
Update #2
Larry’s ( @Cowhunter ) 005A is currently setup in 208V 3 phase
His shop is connected to L1 and L3 and those two phases are used to power AVDR 054 which are also used for voltage reference during regulation.
The primary consumers in his shop are 17 fluorescent light fixtures with 6 pcs T8 Bulbs for a total of 102 Bulbs and at least 17 very large sized ballasts.
Then 4 heaters with 5.3 KW rating @240 V
All turned on looks like this on MeBay
the actual load on genhead is 71% of 30KW
we configured the overload / overcurrent setting so it will trip after 10 seconds with over current alarm
20,535
Update #2
Pretty Amazing how much load those Ballasts draw. We have (had) 45 four foot T-12 fixtures in our offices. About 6 years ago, we bought T-8 Florescent Replacements with LEDs. That naturally eliminated the foot long and four inch wide Ballasts. Saw a heck of a reduction on office power... Can't imagine what the draw would be if several ballasts were to go out at the same time (They seem to do that...)
