shadow
Member
- 116
- 1
- 18
- Location
- Cedar Rapids, Iowa
I am hoping to make a portable unit using my 10kw genset and Hydrovane compressor and a Thermal Dynamics plasma cutter I’m getting. I don’t know if I can power the stuff with the genset. I know the compressor is 220v but I don’t remember the phase. The plasma cutter shows powers of:
[The following Link Diagrams for 208/230/460, 230/460/
575, and 220/380/500 volt transformers are shown below.
For 380/415/460, 380/460/500, and 180/200/220]
I am not an electrician and I am totally confused reading all the numbers. The 10kw genset is MEP-018A. It states:
The Model MEP-018A generator is 60 hertz. The voltage rating is120/240 and 120, 1 phase and 120/20 8 and 120, 3 phase to voltage ratings. The amperage is 3 phase connection load current, 34.7 amperes per line, 1 phase connection load current, 104 amperes and 52 amperes load current on 240 volt connection.
The plasma cutter manual states:
80 kVA, 50/60 Hertz, three-phase in the following
standard voltage/amperage combinations:
(It then shows a chart)
Input voltage: 208
Amperage: 320
It then lists:
Rated Output
400 amperes, DC Straight Polarity at 200 volts
Current Control
50 to 400 amps continuously adjusted
Feedback control circuit stabilizes cutting current
Control Circuit
24 volt AC
How do I figure out the amp output of the genset?? If I’m reading right, the plasma cutter needs 320amps and 208volts. Or is the 320amps referring to output at the 208volts input? I am so lost right now.
The compressor has to run at the same time as the cutter so I can't switch back and forth. I only have one genset.
Can anybody shed some light on if the 10kw genset will work.
[The following Link Diagrams for 208/230/460, 230/460/
575, and 220/380/500 volt transformers are shown below.
For 380/415/460, 380/460/500, and 180/200/220]
I am not an electrician and I am totally confused reading all the numbers. The 10kw genset is MEP-018A. It states:
The Model MEP-018A generator is 60 hertz. The voltage rating is120/240 and 120, 1 phase and 120/20 8 and 120, 3 phase to voltage ratings. The amperage is 3 phase connection load current, 34.7 amperes per line, 1 phase connection load current, 104 amperes and 52 amperes load current on 240 volt connection.
The plasma cutter manual states:
80 kVA, 50/60 Hertz, three-phase in the following
standard voltage/amperage combinations:
(It then shows a chart)
Input voltage: 208
Amperage: 320
It then lists:
Rated Output
400 amperes, DC Straight Polarity at 200 volts
Current Control
50 to 400 amps continuously adjusted
Feedback control circuit stabilizes cutting current
Control Circuit
24 volt AC
How do I figure out the amp output of the genset?? If I’m reading right, the plasma cutter needs 320amps and 208volts. Or is the 320amps referring to output at the 208volts input? I am so lost right now.
The compressor has to run at the same time as the cutter so I can't switch back and forth. I only have one genset.
Can anybody shed some light on if the 10kw genset will work.