Not yet...When I got it the genset it didn't run. After cleaning the tank, a couple of new hoses, and installing a new pump with an injector block cleaning it runs great now. I then proceeded with testing the generator. It runs with no faults and has 120/208 readings on gauges and one side of the contacts. I have readings before the output terminals, just not at the output terminals. I pushed the interrupter button and it lit up.
What do you by mean, "I pushed the interrupter button and it lit up" Do you mean you pushed the DS-7, (AC interrupter light?) and the press to test function lit the light up?
When I close the interrupter switch nothing happens (contacts don't engage). I pulled the contacts and it tested good (contacts pull in with 24v and have .3 ohms across the contacts). I then proceeded with the interrupter switch testing. Pulled it and tested per TM and got bad readings. Apologize for the long story lol.
Long stories are better. More info.