Drash 28kw w Isuzu 4cyl diesel putting out extremely low power or none at all.. ANY HELP WOULD B MOST APPRECIATED
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
I’m new to this site I’m wondering why I have no response 0 ? Wrong category?..not enough info? Can someone help out the rookie??Drash 28kw w Isuzu 4cyl diesel putting out extremely low power or none at all.. ANY HELP WOULD B MOST APPRECIATED
That’s correct after the HP-2 there’s 185/TMSSThere are more models than grains of sand on the beach. I think you need some paint remover.
NSN: 8340-01-533-5396
Ser, # N26-11899-001 (I think)
Model # HP-2
filetype:pdf "8340-01-533-5396"
filetype:pdf "11-6115-742-13P"
filetype:pdf "11-6115-742-13&P"
Where can I find that manual ? I looked on here but I quite possibly overlooked it. Fuse was good ready to do the test to bypass regulator… your help is greatly appreciated brother thank youIn their nomenclature 185 is an 18kW with a 5 ton ECU,,,HP-2 is the trailer size. there is also an HP-4, 6 and 8....they carry more weight
If you have no voltage or low voltage you need to be sure where the fault lies...is it making voltage but not coming out of the breakers? Breakers can fail high resistance ....get to the generator head and see if it is actually making anything...if not, start with the SE350 voltage reg, check the fuse hidden on the back of the reg, if good, download the SE350 Marathon manual and look at constant excitation test...
That is a test you can do which will prove to you that the generator is capable of making voltage and being stable. That will put your mind at rest that the issue is the regulator.
If you unhook F+ and F- from the regulator then carefully attach the wires you pull off to a 12 volt battery. F+ to positive, F- to negative...That removes the regulator from the circuit and pushes 12vdc down into the generator. Leave wires connected and restart engine...voltage should shoot up to around 220 VDC and be stable...Basically the battery is taking the place of the regulator and exciting the field in the generator to make voltage.
When I do this test I use wires with an inline fuse as the car battery I have for the 12volts has way too many amps for safety if the wires ground out by accident....really recommend you use fuse or circuit breaker on battery wires.
Reconnect F+ and F-... if it made voltage on test but now not again, check fuses but likely regulator is dead. If not, you will have also flashed the field in the test and it should be working....
Be careful...read the reg manual till it makes sense...
Regards
Poccur
Use your favorite search engine to search something like the following;Where can I find that manual ? I looked on here but I quite possibly overlooked it. Fuse was good ready to do the test to bypass regulator… your help is greatly appreciated brother thank you
Thanks for all the help brotherUse your favorite search engine to search something like the following;
marathon se350 manual
In my case the top hit gets a link to the Marathon website with it;
All the best,
2Pbfeet
I WANTED TO THANK ALL MY BROTHERS THAT HELPED WITH THIS!!! I RAN THE TEST YESTERDAY identified that the regulator was scorched and generator was making steady power.. without the help from the real people on this site . This steel soldier would be dead…. Thank You. JKDrash 28kw w Isuzu 4cyl diesel putting out extremely low power or none at all.. ANY HELP WOULD B MOST APPRECIATED
Thanks brother I’m going to msg himThe unit you have is rare and not very many people deal with them. Im one of the few. POCCUR is the expert on any HDT HVAC unit. He developed and worked for HDT and he has helped me tremendously over the years. The manuals are not available, only from HDT.
Where can I find that manual ? I looked on here but I quite possibly overlooked it. Fuse was good ready to do the test to bypass regulator… your help is greatly appreciated brother thank you
Thank you VERY MUCH for the advice and tech support. I’ve purchased a new VR it’s a besler BE 350 roughly 400$ less than the 350 marathon. For this 18kw/5 should it be set for 50 or 60Hz the marathon was set @50 is it possible this is what scorched it?? Any advice for installing the new one? Can’t really afford to cook another VR… again THANK U for your information and help J.In their nomenclature 185 is an 18kW with a 5 ton ECU,,,HP-2 is the trailer size. there is also an HP-4, 6 and 8....they carry more weight
If you have no voltage or low voltage you need to be sure where the fault lies...is it making voltage but not coming out of the breakers? Breakers can fail high resistance ....get to the generator head and see if it is actually making anything...if not, start with the SE350 voltage reg, check the fuse hidden on the back of the reg, if good, download the SE350 Marathon manual and look at constant excitation test...
That is a test you can do which will prove to you that the generator is capable of making voltage and being stable. That will put your mind at rest that the issue is the regulator.
If you unhook F+ and F- from the regulator then carefully attach the wires you pull off to a 12 volt battery. F+ to positive, F- to negative...That removes the regulator from the circuit and pushes 12vdc down into the generator. Leave wires connected and restart engine...voltage should shoot up to around 220 VDC and be stable...Basically the battery is taking the place of the regulator and exciting the field in the generator to make voltage.
When I do this test I use wires with an inline fuse as the car battery I have for the 12volts has way too many amps for safety if the wires ground out by accident....really recommend you use fuse or circuit breaker on battery wires.
Reconnect F+ and F-... if it made voltage on test but now not again, check fuses but likely regulator is dead. If not, you will have also flashed the field in the test and it should be working....
Be careful...read the reg manual till it makes sense...
Regards
Poccur
They are simple to install. Just wire it in like the one you took out (you might want to buzz it out also, 3+4 are phases, F+ and F- go to generator head) If the generator was US then the 18kW would have made 208 so you need 60Hz...Thank you VERY MUCH for the advice and tech support. I’ve purchased a new VR it’s a besler BE 350 roughly 400$ less than the 350 marathon. For this 18kw/5 should it be set for 50 or 60Hz the marathon was set @50 is it possible this is what scorched it?? Any advice for installing the new one? Can’t really afford to cook another VR… again THANK U for your information and help J.