Hello guys,
A little while ago there was a thread talking about errors found in the generator TM's and we had discussed potentially creating Sticky's for these Errors.
I came across another error recently and it mad me remember that thread and wonder what happened to it.
In this instance I was building an AC control box out of parts I have on hand for an 003 for another SS member who's box was ransacked by it's previous tenants ( mice )
After building it up and testing it, I noticed there is a picture of the CVT winding in the -34 TM which shows 3 wraps of each pair of wires through the CVT holes.
The correct wire wrap is 8 conductors total through each hole for an 002 and 4 conductors total for an 003 box.