Previous post updated.Since you provided the solution, for which MEP does this apply? They make several auto/remote start kits from MEP-002a to MEP-806b.
Sorry - should have posted the solution.
For the Inovahightech autostart controller board one the MEP803a or MEP802a without the K-Ext relay for cool down the following connections need to be made in order for the controller board to engage the load after the time interval set by the dip switches. This is not clear from the current installation documentation provided on the Inova website. Peter provided me with the needed connection information.
Connect TB#10 from the autostart controller with terminal K8-12
Jumper TB#9 and TB#1
My particular setup has another breaker switch between the panel which also provides me with gauges that reads Volt, Amp, Kilowatt and Kilowatt hours on the generator side of the switch. This allows me to see when the circuit is energized on the generator which then allows me to close the feed to my electric panels after I have disconnected the main feed and the manual interlocks allow me to switch the generator backfeed on to the panels. Load balancing is done manually and the aforementioned gauges allow me to see how much load is on each circuit. The panels and switch are located inside my garage which I have access to when we're all boarded up and strapped down when a hurricane rolls through the neighborhood. I activate the autostart with a RF remote relay installed inside the MEP which applies +24V DC current to the TB#3 connection.
Hope this helps.
What breaker switch are you using that has volt, amp, and kw gauges on it?Sorry - should have posted the solution.
For the Inovahightech autostart controller board one the MEP803a or MEP802a without the K-Ext relay for cool down the following connections need to be made in order for the controller board to engage the load after the time interval set by the dip switches. This is not clear from the current installation documentation provided on the Inova website. Peter provided me with the needed connection information.
Connect TB#10 from the autostart controller with terminal K8-12
Jumper TB#9 and TB#1
My particular setup has another breaker switch between the panel which also provides me with gauges that reads Volt, Amp, Kilowatt and Kilowatt hours on the generator side of the switch. This allows me to see when the circuit is energized on the generator which then allows me to close the feed to my electric panels after I have disconnected the main feed and the manual interlocks allow me to switch the generator backfeed on to the panels. Load balancing is done manually and the aforementioned gauges allow me to see how much load is on each circuit. The panels and switch are located inside my garage which I have access to when we're all boarded up and strapped down when a hurricane rolls through the neighborhood. I activate the autostart with a RF remote relay installed inside the MEP which applies +24V DC current to the TB#3 connection.
Hope this helps.
You need to expand the detailed description below the listing for the full specs. They are 50-60Hz.The gauges are exactly what I was curious about. The description lists them as 50 Hz meters though. They work ok and match hand held meter?
As for the question about n accuracy - I have not compared with a multi meter. Nearest 2 amps / 500watts is good enough for me to balance loads.The gauges are exactly what I was curious about. The description lists them as 50 Hz meters though. They work ok and match hand held meter?
On the inverter generators they use this one.Ok that is exactly what I needed to know. I have been looking for something like the gauges, but I use a MEP 831 for outages that require only a little power. Someone correct me if I'm wrong, but I believe that would be considered inverter tech and would not work with these gauges
I use a Kill-a-watt plugin meter to confirm voltage and frequency on an outlet. The others just gives me bolts, amps, kilowatt and kilowatt hour per branch. Frequency is not likely to be different per branch.Ok I did a little digging and those weren't exactly what I was looking for. Maybe they don't make what I want. I'm looking for voltage, Hz, and amps on one gauge that can be used on inverter (831) and up to 80 amp capacity for the 803. Back to the drawing board!
What about wiring an outlet into the generator circuit before the panel and plugging in a Kill-a-watt.Thanks. I did find that one earlier. It doesn't say if it will work with inverter type power that I can see. I sent them a message to see anyhow. I don't need frequency on both lines. I'd just like to be able to monitor it without going out through weather 125' away to see gauges. I plan on installing the same remote board you did and would like to make sure everything is right before turning the breaker in the house. That rules out using a plug in meter since the panel would have to be energized.