Hello,
I stumbled upon this forum a while back and finally had to sign up, there is so much great information here! We have been buying, selling and using surplus equipment for many years. We have a few MEP-002As laying around and I finally wanted to set one up at my house for back-up power. So I cleaned up and serviced two of them, brought one home and are getting ready to sell the second. Below are links to videos of load testing the gensets.
For the load test I just used what I had laying around. I used a 6kW 240V immersion heater and a 8KVA variable transformer to varying the load to the generator. I used ohms law to determine the resistance of the heater was 9.6 ohms. The Powerstat uses the generators 240V single phase output as its 240V input. The output of the powerstat is 0-280V. As seen in the video I made a chart of power consumption at a given voltage. At 240V the heater is using 6000Watts, at 250V it is using 6500watts, and so on.
http://youtu.be/1ybDw8XPSVY - Gen A (500 hr unit) - 8 kw test
http://youtu.be/0HKuWg8dzsE - Gen B (1500 hr unit) 6 kw bog down test
Basically the results are that generator A (the 500 hr) unit coult take a full load at 8,342 watts without skipping a beat, I was very impressed on how good it sounded. Generator B (the 1500 hr unit) works fine at 6000 watts, but as I increased the load from here it would start to bog down, and anthing over 6500 watts was too much and it would bog to a stall if I didnt prevent it. So what is wrong with Generator B? I do notice when being run hard it smells like it is burning oil. In all honesty if the problem cant be adjusted or fixed within 2 hours I think it would be easier to swap in one of these rebuilt crate engines we also have.
PS. I am aware that the test wattage numbers may not be fully accurate without an amp meter due to some theoretical assumtions.
Any ideas.
Thanks,
Kendrick
I stumbled upon this forum a while back and finally had to sign up, there is so much great information here! We have been buying, selling and using surplus equipment for many years. We have a few MEP-002As laying around and I finally wanted to set one up at my house for back-up power. So I cleaned up and serviced two of them, brought one home and are getting ready to sell the second. Below are links to videos of load testing the gensets.
For the load test I just used what I had laying around. I used a 6kW 240V immersion heater and a 8KVA variable transformer to varying the load to the generator. I used ohms law to determine the resistance of the heater was 9.6 ohms. The Powerstat uses the generators 240V single phase output as its 240V input. The output of the powerstat is 0-280V. As seen in the video I made a chart of power consumption at a given voltage. At 240V the heater is using 6000Watts, at 250V it is using 6500watts, and so on.
http://youtu.be/1ybDw8XPSVY - Gen A (500 hr unit) - 8 kw test
http://youtu.be/0HKuWg8dzsE - Gen B (1500 hr unit) 6 kw bog down test
Basically the results are that generator A (the 500 hr) unit coult take a full load at 8,342 watts without skipping a beat, I was very impressed on how good it sounded. Generator B (the 1500 hr unit) works fine at 6000 watts, but as I increased the load from here it would start to bog down, and anthing over 6500 watts was too much and it would bog to a stall if I didnt prevent it. So what is wrong with Generator B? I do notice when being run hard it smells like it is burning oil. In all honesty if the problem cant be adjusted or fixed within 2 hours I think it would be easier to swap in one of these rebuilt crate engines we also have.
PS. I am aware that the test wattage numbers may not be fully accurate without an amp meter due to some theoretical assumtions.
Any ideas.
Thanks,
Kendrick