So this is a new one for me. I have a customer that bought a generator from me 2 years ago. He started it recently and after 5 minutes the voltage went to 0. Told him to take 17 off VR and voltage spiked so assumed voltage regulator. He purchased a new one from Triple Jim adn installed. Voltage returned but after a few minutes voltage and hertz went to 0. So he brought it to me. When I first start it voltage is perfect, start load testing and after you get to 14kw voltage starts to drop from 120 down to 106 and falls to 105v. Can let it run about 5 minutes under load and it looses voltage and hertz again.
I tested T1, T2, tried another known good VR. All Good. Replaced the linear reactor because it was slightly out of spec. Still same issues. Only thing that I can think is left is CVT1. Has anyone seen this before
I tested T1, T2, tried another known good VR. All Good. Replaced the linear reactor because it was slightly out of spec. Still same issues. Only thing that I can think is left is CVT1. Has anyone seen this before