MEP 004A / 005A / 006A Day Tank Fuel Level Switch repair

peapvp

Well-known member
Steel Soldiers Supporter
1,172
1,381
113
Location
Basehor, KS
While working on an other unrelated topic (Retrofitting 005A with MeBay Controller DC70DR MKII, see separate thread), Larry ( @Cowhunter ) encountered some problems with his fuel delivery system. Looking from a retrospect, this issue must have existed for quite sometime and from a time prior to Larry acquiring this Genset a few years ago.

I have not come across any previous threads describing a repair of this Fuel Level Switch, but such a thread may exist here in this forum and I am sure Guy ( @Guyfang ) could write a book about this Switch assembly.

Anyway, here is a short explanation of what happened, what we found and how we proceeded:


The issue at hand was a Day Tank which had randomly ran dry, requiring the Start Switch to be placed in run and Battle Short active to prime system and fill Day Tank, then came the task of getting the air out of the IP System.

After Checking Day Tank Solenoid, Fuel pumps and Fuel Cut Off Solenoid, we discovered the source, the Fuel Level Switch.

The Fuel Level Switch is rather a assembly of two normally open reed contacts (switch), labeled in the TM's as FO-1 / FL-1 and FO-2 / FL-2

The two floats contain small round magnets and when at a particular height, depending on the fuel level, close the two contacts in the reed switch through their magnetic field.

Fuel Level Switch marked as # 16 original NSN 2910-00-405-6153 ( with move able float stops ) and the later version NSN 5930-00-405-6153 ( with fixed float stops )

Fuel Level Switch Explosion Drawing.jpg

Shown here NSN 5930-00-405-6153 ( with fixed float stops [ 4x C-Clips ] ) from a eBay listing

NSN 5930-00-405-6153.jpg

The original NSN 2910-00-405-6153 ( with move able float stops )

image00.jpeg

This is the Fuel Level Switch Larry has in its Day Tank

The lower float turns on Reed Switch FL-1 which then activates K8, shuts down running Genset and triggers the Fault Indicator Panel, or so is the theroy

The upper float when in the low position turns on FL-2 which then activates the Day Tank Solenoid through the Half Bridge Rectifier CR 27 and keeps this Solenoid active until float has risen through increased fuel level in tank to its top position at which point Solenoid is turned off. At least, so is the theory.

The actual stop points / limits for each float is adjustable by loosening the set screws on the threaded move able brass stop's.

The upper float to keep day tank at certain variable fuel level has 4 small round magnets. In our case here, they are on the top side ( non ring side ) of this float.

The lower float has two magnets also on the top side ( non ring side ) of this float.

As you can see, the middle and upper stops also have a additional steel ring with a setscrew, which when loosened, allows for adjustment of this steel ring without changing the stop position.

These rings serve, in conjunction with the 4 magnets, the purpose of delaying the movement of the upper float to add additional time for Solenoid to be active, providing a slight overfill over the top of the float at stop position.

However, some Genius had installed the top float upside down, as the 4 magnets should attache the float magnetically to the center stop. The release force, which increases with rising fuel level, can be adjusted by rotating the steel ring up or down on the threaded part of the respective stop and is secured in place by means of the setscrew on steel ring.

In our case, the magnets where holding the float to the top stop, which turns FL-2 off, not allowing therefor for FL-2 to close and activate the Day Tank Solenoid.

Normally the lower Switch, FL-1 should then eventually shut off Genset when the level in day tank is low enough, but not completely empty.

The lower switch FL-1 does not utilize the magnetic delay of action since it has only two magnets. It is allowed to move freely in real time with actual fuel level.


And this is where it got tricky. FL-1 would either turn on constantly or not at all, allowing Day Tank to be drained completely without stopping a running Genset.


We therefor proceeded to take the entire assembly apart:

image3.jpeg


We can now clearly see the two reed switches after Larry cleaned the old coating off with MEK and scraped out the outer brass tube from the broken down, gummy silicone rubber filling.

The lower switch is FL-1 and has two black wires connected, which connect to PIN C and D on socket. The upper switch is FL-2 and has two white wires connected, which connect to Pin A and B on socket.

We can also clearly see the bare wire on the lower connection.

Because of the age of this device ( 40 to 50 years old ), the internal Silicone Rubber filling had broken down and this end was making intermittent contact with the outer brass tube, causing the K8 not turn on.

These are the detail pictures of the two switches

FL-1 ( Low Fuel Shut Down )

image13.jpeg

FL-2 ( Day Tank Fill )

image12.jpeg


Note: both contacts are open even though the appear to be closed / making contact

After carefully inspecting and testing everything, Larry used 3/8" 2:1 Shrink Tubing with no glue to reassemble the Switch assembly

image2.jpeg


We then adjusted float stops and made sure top float had the 4 magnets on the bottom side of float.

Now the Day Tank system is working correctly again with the MeBay Controller.

Note: we left the Day Tank Solenoid Circuitry as it was originally, only applying 24V thorough our Fuel Relay ( see Mebay Thread )
 

Guyfang

Moderator
Staff member
Moderator
17,589
26,064
113
Location
Burgkunstadt, Germany
Peter, you described this wonderfully! Few people grasp how this FL-1 and FL-2 function. Or how to screw it up. I have seen this problem more than a few times. And the older the sets get, the more common this happens. Some folks mean well, but do not pay attention to how they took it apart. I have seen them reinstalled like you found it. I have seen the floats in the reversed position. FL-1 on top, and FL-2 on the bottom. I have seen floats from other types of switches installed on this type switch. I have seen JP-4 "eat" the floats up, and the magnets fell out and were attached to the bottom of the day tank. The origanil floats were made of a soft material and JP-4 simply turned it to powder

Back in 1977 when this gen set first came out, the Day Tank was one of our biggest problems. The floats were crap. The contacts became welded together. They arced so much, that they burnt the contacts off. The glass broke. It simply drove us insane. I did just what you did. Took em apart and often tried to make one from 2-3 switches. There is also a switch that fits these gen sets, with only one float. The trip points are farther down in the rod.

The TROSCOM and later CECOM fixed the switches so they became fairly dependable. The L-2 solenoid is bomb proof. Rarely fails. The next big problems we had to deal with was the CR-27 diode mounted next to the L2, on top of the Day Tank. The first few years it was a high failure point on the Day Tank. The diodes failed often. Then lots of folks got the new CR-27 wired wrong. Its only 4 wires, but happened often. The wire harness to the Day Tank and other components was always a spot to check for broken or loose wires.

Great write up!
 

Scoobyshep

Well-known member
1,327
2,019
113
Location
Florida
Excellent indeed.

I have worked with many "2 wire electricians" for those of you who dont know, if its more than 2 wires they will mess it up.


Float wise I worked on a system that had about 30 floats similar to these. they were housed in jar type enclosures. The problem was the things in the water would leave UHMW shavings (Ultra High Molecular Weight(think plastic)) and they would clog the floats. This was bad enough to warrent a monthly tear them down and clean floats PM. EVERY MONTH these people would inevitably put a float together backwards and not check the idiot lights.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks