I followed along on generatorshawn's post as it seems identical except for a couple of the readings.
I have no cables attached to the machine.
I can not use the battle short to close the circuit breaker.
I am not running in parallel and I have flipped the switch a couple of times to confirm.
I metered between 8-7 on the K15 and 8-ground and 7-ground all 0 volts
I metered between 5-6 on K14 and measured 4.9 volts
5-ground 0 volts and 6-ground was 4.9
metered between pin 6 on K14(wire p62h1 and pin 8 on K15(wire p61A1 it measured 0 volts.
If I need to do anything else please let me know or point me in the right direction. I have read through the TM's and the wiring schematics are basically gibberish. I appreciate any assistance. Thank you.