Harleyd315
Member
- 195
- 5
- 18
- Location
- Denville,New Jersey
I have an 003 that I aquired for our FD. I did all my usual pre start checks and got it running just fine. I went to hook up my load bank in 3 phase to do a load check and had no power on L2 nor would the % of load meter work. I took the side covers off and checked for loose or missing wires,all was good. I then put the gen in 120/240 mode and had current to L1,2,and 3. I rotated the voltage switch multiple times it snaps into each position fine. I thought maybe the arrow knob on the switch was reversed but found out that it is indexed and only goes on one way. So 208 3ph is where 120/240 single phase is and vise versa. The question is, can this be fixed by changing some wires easily or should I just remark the knob and leave it alone?