We have a MEP805B generator. With the voltage selector switch set for 416V the generator starts and runs (voltage is very low on the CID 365v range) with no response from the voltage up down switch(frequency does move with switch). With the selector switch on 208v the generator starts briefly then errors with an over voltage error and shuts down.
Now I think the AVL-100 Voltage regulator needs to be replaced/ repaired however we have found a burnt K23 relay (Pins 3 and 6 to be exact). Reading the technical manual on page 4-111 the voltage between P9-5 and P9-6 is 214VDC (should be 8vdc). With the Voltmeter on AC it reads 120VAC as well (same terminals). Also found the resistor R6 is 120 Ohms (Should be 40 Ohms).
The AVL-100 powers up AC sensing light is on, DC supply lights on, and Field Voltage light is on.
So a couple of questions. This is a "new to us" generator and we have yet to get it running correctly.
1. If the AVL-100 needs to be replaced does anyone know of an exchange program or a repair service we can send the module in to?
2. Is there anything we need to do prior to installing a new AVL-100?
3. Where could this 214 vdc/ 120vac reading be coming from?
4. Is there anyone that I can call that can help me get this thing sorted out? (Hoodsport, Wa area)
Thanks in advance
Brian
Now I think the AVL-100 Voltage regulator needs to be replaced/ repaired however we have found a burnt K23 relay (Pins 3 and 6 to be exact). Reading the technical manual on page 4-111 the voltage between P9-5 and P9-6 is 214VDC (should be 8vdc). With the Voltmeter on AC it reads 120VAC as well (same terminals). Also found the resistor R6 is 120 Ohms (Should be 40 Ohms).
The AVL-100 powers up AC sensing light is on, DC supply lights on, and Field Voltage light is on.
So a couple of questions. This is a "new to us" generator and we have yet to get it running correctly.
1. If the AVL-100 needs to be replaced does anyone know of an exchange program or a repair service we can send the module in to?
2. Is there anything we need to do prior to installing a new AVL-100?
3. Where could this 214 vdc/ 120vac reading be coming from?
4. Is there anyone that I can call that can help me get this thing sorted out? (Hoodsport, Wa area)
Thanks in advance
Brian