RPM's good But not showing on panel meter, Unit will not produce correct voltage - about 25v (set on 20 an slowly goes up to 100v with switch in start position after running. Followed manual instructions and tested the "droop transformer" by making a quick brine load bank - the test showed only .2A ac produced by transformer - if I tested correctly. When the manual says to make 10 passes with 10ga wire - can I just wrap it around the coil (and of coarse thru the window) 10 times or does that make for a bad test by creating some kind of inductor?
Any thoughts on the test and or the problem is appreciated
Any thoughts on the test and or the problem is appreciated