Meps 1060 generator problems

Ghostrider65

New member
3
0
1
Location
Hawaii
Aloha guys, I have a 2015 MEPS 1060 Cummings diesel Generator, it was working fine but now I keep getting a 1452 error code, and in the manual it doesn’t really tell how to fix it. I was wondering if somebody would be so awesome to help me figure out this problem, it’s a 30 K generator and the Cummings diesel works great starts right up, but as soon as I hit the AC interrupt, I get the error code and unit shuts right down. Any help or suggestions would be so much appreciated. Thank you..
 

Ghostrider65

New member
3
0
1
Location
Hawaii
Fault 1452 indicates that the DCS did not get the contactor closed signal from the contactor after you pressed the contactor open/close button.
Possibly your contactor has failed or there is a wiring problem between the DCS and the contactor.
The -24 TM has the troubleshooting steps for this issue.
Thank you so much , I wil see what I can do, T
 