Paralleling two or more MEP 002A or 003A
peapvp
1,152
Basehor, KS
I did this Video Tutorial today. I really don't want to rain on any ones parade, but I thought I might put my 25 cents in on this one.
But there are three ways of doing this:
The wrong way - it somehow works way and a right way of doing this
This Part 1 of 4 - I will do the other parts as time permits.
http://youtu.be/kgR-gEquVqs
Munchies
Keesler Air force base/ MS
You had me right until digital control. I think thats the BEST way, but the 004-007 are basically using the 'lightbulb' phase sync method and you are instructed to flip the control switch for the contactor. The only difference in my mind between an 002/003 and an 004-007 is that the 004-007 use the control lead between sets to slave the voltage regulators. But how precise is this? Major benefits here being that the slaved VR's can respond with loads being applied and removed keeping the voltage the same.... Good talking points.
edit. watched the rest, you did touch on common control..
If i was going to make one I would add in contactors on both and have the parallel board close it for me for simplicity sake.
LuckyDog
11
Freedom, NH
Dupe Thread:
Sewerzuk already showed how to parallel the 002 and 003:
Here
I can't see the video due to firewall at work. Pics and Videos are always good though.
Just curious, if there are 3 ways to do it, why is there 4 parts? :rolleyes:
And are you going to really show the "Wrong Way"? :razz:
peapvp
1,152
Basehor, KS
Thanks for the comments
Here is what we are going to cover in the other Video Tutorial Parts:
Part 2: Theory of synchronizing and locking in the Output Frequencies, discussion of general problems of paralleling Generators with two or more independent Governors
Part 3: Operating both Voltage Controller Boards from one Potentiometer / Rheostat - explaining the wiring changes and parts needed
Part 4: A Simple automatic switch to connect the 2nd(3rd etc) Generator at exactly the right time and modifying the Governor system to assure locked and synced operations, even under heavy load - explanation of circuit, wiring changes and parts needed
each part is going to be between 10 to 20 minutes - that's why I broke this up into four parts
Munchies
You are absolutely correct re the timing and light method, but I think one thing is being overlooked perhaps.
There is a decent amount of wiggle room, and as long as your are more IN phase than out, after flipping your breaker you lock the rotors together effectively. When this happens it will not lock each right where its at, it will violently speed or slow both sets very slightly and lock them perfectly in phase. This is why the military equipped the 004-007 sets with dual phase indication lamps and is done by looking at the lights and flipping a switch to close the main contactor. The slight mismatch in voltage between sets is a much bigger concern, but can be fixed as mentioned by tying the VR's together.
peapvp
1,152
Basehor, KS
I am currently quite busy and the remaining videos will have to wait a couple more weeks.
PeterD
Jaffrey, NH
Just to add, I know another MEP-003 user who parallels them. He only does it if he has to, but he can do it. Once paralleled they stay in sync until either the connection is broken or you have some mechanical failure.
3dAngus
101
Perry, Ga.
Just curious, what is the hazard if there is a failure in one of the two MEP-002s.
If the VR went out and voltages fell from 120v to 100v, would this create a house brownout?
Any other risks?
peapvp
1,152
Basehor, KS
If the VR goes out then the generator will not produce any Voltage anymore. The excite Voltage collapses and that will trip the circuit breaker of the unit which is still running. This situation is not as bad as two gensets paralleled with a small voltage difference. This situation will overheat the lower voltage generator and burn the coil over time (usually several ten's of minutes) without tripping the circuit breaker of the higher voltage genset. See my first video of this series in a post below(above).
peapvp
1,152
Basehor, KS
I wanted to add the formula on how to calculate the currents flowing in an unbalanced parralled Genst last night, but my sausage fingers were to big for my Android Tablet with it's touchscreen.
So, I am going to post it now from my PC. I like when guys like 3DAngus ask questions.
The internal Resistance of the Generator Coil is 0.1 Ohm for both Units 002A and 003A
I would like to give you the formula based on 3DAngus question about the 120Volt to 100Volt imbalance:
First we subtract the lower Voltage form the Higher Voltage:
120VAC - 100VAC = 20 VAC Differential Voltage
Secondly, now we can calculate the current flow with Ohms Law:
I = U/R where U=20VAC and R=0.1Ohm Internal Resistance
I = 20/0.1 = 200 Amps
This will trip the breaker definetly on the Higher Voltage Generator almost instantaneously - meaning no damage to either Genset
another example:
120VAC - 116VAC = 4VAC
I = 4V/0.1Ohm = 40 Amps
This example will not trip the Circuit Breaker, depending whether or not there is an additional load attached to the paralleled Gensets. Assuming a no external load condition, this paralleled Genset Pair will get damaged within less then 20 minutes of operation due to overheat of the coil.
Again, a small Voltage difference between say 1Volt to 5 Volt will most likely not trip any Circuit Breaker since the Amp Values are to small, but will cause the Coil on the Genset with the lower Voltage to burn out over time.
peapvp
1,152
Basehor, KS
Original Video Part 1 posted 12.08.2013: Introduction to Paralleling Generators (prim
Back by popular demand. I had inadvertently made changes to my YouTube channel and deleted the 4 videos
This is the original Video Part 1 posted 12.08.2013: Introduction to Paralleling Generators (primarily 002A and 003A)
This was pre-HD......
https://youtu.be/6UuEonP4qAY