Pics of the job i did with the MEP 803a with the inova auto start kit plus ATS

titoveli

New member
20
0
0
Location
the valley, Anguilla
The gen set bonding connector is still connected. Is this a house connected gen set?
it is connected to a a house. i dont understand the rest. this the job i did with pics of the auto start kit and relay all working perfect got voltage now on the lugs going stright the the ATS but the ATS has a problem i will get it fix in the coming days already email the guys i both it from
 

Zed254

Well-known member
866
466
63
Location
S. Hampton Roads, VA
https://www.steelsoldiers.com/showthread.php?164386-Trailer-Mounted-MEP803a-Grounding

Good discussion on grounding your generator and the SINGLE ground to neutral bond in your home's electrical system.

Last picture, lower right side: the bonding strap is still in place between the generator's ground and neutral. This is correct if it is a stand alone system.....you are out in a field and your generator is powering some work tools. Your home already has a neutral to ground bond in the breaker box....or should. You only want 1 ground to neutral bond in your home's electrical system. If your generator will only be used as a home back up you should remove the generator's ground to neutral bond.
 
Last edited:

titoveli

New member
20
0
0
Location
the valley, Anguilla
https://www.steelsoldiers.com/showthread.php?164386-Trailer-Mounted-MEP803a-Grounding

Good discussion on grounding your generator and the SINGLE ground to neutral bond in your home's electrical system.

Last picture, lower right side: the bonding strap is still in place between the generator's ground and neutral. This is correct if it is a stand alone system.....you are out in a field and your generator is powering some work tools. Your home already has a neutral to ground bond in the breaker box....or should. You only want 1 ground to neutral bond in your home's electrical system. If your generator will only be used as a home back up you should remove the generator's ground to neutral bond.
no here we only bond the ground to neutral in the meter box not at the panel. i will take it off anyways cause its the same thing
 