Do you have a plan to be able to vary the anti wet stacking load depending on what your amp draw is at that time or just going to use a timer to add in an additional fixed load at certain intervals? Using either a bank of heating elements and relays to cut them in or a braking device on the shaft?
"be able to vary the anti wet stacking load depending on what your amp draw is at that time"
This would be very simple but i went a bit further. I did not want to waste fuel by running the gen hard all the time when it may not be needed to prevent wet stacking.
It sounds like it may not be worth it for the MEP002/3 but would it be worth it for the water cooled units?
My plan was to program an Arduino or something similar to monitor the current from both lines coming from the generator. It would monitor the loads to help balance them and to help prevent wet stacking.
To prevent wet stacking it would monitor for the current and make sure that the generator had a load greater than the load needed to prevent wet stacking for the amount of time we determined it needs to prevent that wet stacking. If it needed to it would add loads to the unit using relays. Each relay can add 300 - 3000 kw depending on the setup. I was looking at a total of 3 relays for each leg.
It would trigger as many relays needed to meet the load demand of the generator to prevent wet stacking.
So example
Power is out for 24 hours we want the generator to run 80 percent load or 75 amps for at least an hour in a 8 hours period. During the day when everyone is up the power is over the required load for 1 hour as it is normally operating. So it would not need to add power to help it meet that need. However night comes and the generator is getting to that 8 hours and has only ran at 40 percent load. So it would add loads to make sure it gets over that 80 percent load for those 8 hours. After it meets the requirement it will take off the added loads again. If it is being loaded by the Arduino (or whatever device) to help meet the load need for that 8 hours. If all of the sudden someone kicked on a high output appliance. it would turn off relays to let the natural load from the house be used to meet that 80 percent load.
The relays would be simply on and off switches for outlets to run heaters or other power consuming devices. Or you could modify the relay setup to operate a load bank.