bimota - I stand corrected - - another victim of CRS disease. I had to do some digging since it has been a while since I originally found the info and my fuzzy memory had it all wrong.
"4.3.7 Motor Starting Capability. The Class 1 (precise) 15-200 kW dieselengine-driven generator sets are capable of across-the-line starting of a motor
rated at one horsepower per kW of set kW rating. The class 2 (utility) 15-200
kW diesel engine-driven generator sets are capable of across-the-line starting
of a motor rated at one horsepower per 1-1/2 kW of set kW rating. The starting
current rating of the motor is NEMA Code F and the motor being loaded with a
flywheel having the inertia equal to that of the motor. Starting is defined as
acceleration of the motor to rated speed without tripping any safety device."
Taken from MIL-STD-633E. Apparently not a "standard" anymore, though.
"NOTE: MIL-STD-633E has been redesignated
as a handbook, and is to be used for guidance MIL-HDBK-633
purposes only. This document is no longer to be 20 FEBRUARY 1998
cited as a requirement. For administrative expediency,
the only physical change from MIL-STD-633E is this
cover page. However, this document is no longer to be
cited as a requirement. If cited as a requirement,
contractors may disregard the requirements of this
document and interpret its contents only as guidance."
Also note this does not include the smaller sets(below 15KW).
My machine shop is full of 3-phase equipment, so I will have to test this info at some point. I did this at one point with a good running 005a. It would start my 10 HP air compressor, but not my 25 HP Lucas boring mill or my 15 HP Monarch Lathe. The circuit breaker tripped on both of them. Think it saw the large starting current as a short because it tripped immediately.
My 75KW load bank was originally set up for 400hz service. I replaced the six cooling fans with 60hz models. It has three separate resistance loads available, two 20KWs and one 35KW, which can be applied in any combination, so I can load to 20KW, 35KW, 40KW, 55KW, or 75KW. Make one **** of a good space heater at 75KW!!
Also have electric space heaters for checking the smaller units, 4KW (x2) and one 5KW.
Have not messed with the 180KW load bank yet. As I get the 007 gensets going, I will need it, though.
The generators I have are ones still in my inventory of units for sale, except for the lone 003a. Think I will keep this one.
The 007 units have been a disappointment. Getting coolant in the oil on 2 out of the 3 I have checked out so far. Have had the same problem with most of the 006a units I have had. Not buying any more 006a or 007a set for this reason. Have had very good luck with the 002a, 003a, 004a, and 005a gensets and I really like the 805a and 806a sets. The John Deere engines are awesome. Have seen 55KW from an 805a!
You need to redo your math on the RO machine. Using 30,000 watts instead of 60,000, unless that generator is a 006a.
This is a really useful thread. Thanks to all the participants.