MEP-804A cranks and starts, but does not stay running.
Pain
Pittsburgh, PA
Greetings all!
The problem arises when you change the frequency select switch to 60hz (with the genset off) and attempt to start it in this condition. It will run for a brief moment, until you take your hand off the start switch and it goes to prime and run, where it will then immediately shut down and the “over voltage” fault indicator will light. I should add to this that the engine seems to sound louder/faster when starting it in the 60hz setting.
Strangely when shut off and switched to 50hz, the genset starts and runs momentarily, and does the same as stated above (runs briefly and dies, over voltage lamp lights up). This strikes me as odd, as last week I had it running in the 50hz mode, albeit with some very odd and abnormal seeming readings on my multimeter. Now it won’t even stay running in either selection.
To add more information, In both freq settings I observed the gauge needles moving.
I’m open to any and all advice as the manual hasn’t been helpful with my progress.
Note:
I recently discovered that there is apparently a MWO for this model of genset, where you add a 3 amp fuse to one of the wires on A1.
This brings up another question I have. Would the lack of this fuse modification cause this to occur?
Thank you for reading and I look forward to hearing from others.
-Pain
Tinstar
2,613
East of Edmond, Oklahoma
Download the TM's for your generator and familiarize yourself with them.
Lots of great info.
The generator experts will point you in the right direction.
kloppk
4,206
Massachusetts
Has this generator produced proper power for you in the past?
Or are you troubleshooting a "new to you" generator?
The 3 AMP Fuse MWO simply adds a fuse in one of the leads from the A1 AC Voltage Regulator to the Static Exciter inside the Gen Head.
It's purpose is to protect the gen head from damage should the Voltage Regulator fail sending too much voltage to the gen head. The fuse blows to protect the static exciter from burning up due to a bad voltage regulator.
Shown here is the schematic
The engine will be running at a higher RPM when set to 60 Hz. The AC Output Frequency is directly proportional to engine RPM.
At 60 Hz the RPM is 1,800
At 50 Hz the RPM is 1,500
First I'd suggest getting the MWO installed to protect the Static Exciter from damage. Don't run the set until you get it installed.
After it's installed I'd suggest performing the AC Voltage Regulator Testing as specified in the -24 TM.
Guyfang
27,256
Burgkunstadt, Germany
This is the second thread you have opened on this problem, this gen set. Thats called cross threading, and is not allowed. So please pick one or the other thread, and stick with it. Tell me the name of the thread you will keep using, so I can do away with the thread not to be used.
Pain
Pittsburgh, PA
I’ll head over to the first one I made then (MEP-804A under voltage light) , this is the same model of generator but a different unit.
