35kw Get only putting 50 volts

sfus2645

New member
27
9
3
Location
Miami, Florida
Hi, I have a 35KW GET with a John Deere engine and a marathon generator. The pump was shut, I rebuilt it and work fine now, but it's only putting 50 to 55 volts.
 

87cr250r

Well-known member
1,267
1,991
113
Location
Rodeo, Ca
That's usually the result of a failed voltage regulator, residual magnetism is generating the voltage. Put a load on it and it will drop to zero.
 

jamawieb

Well-known member
1,435
557
113
Location
Ripley/TN
Make sure your connections are tight on the vr. I just had a unit with a similar problem and after wiggling wires that connect to the vr it would produce correct voltage when i held them in the perfect position. Took the vr off and checked the connectors and one was about to fall off the wire. Fixed the issue after replacing the connector.
 

Poccur

Active member
205
143
43
Location
Roanoke, VA
I installed the new VR but it doesn't work either.
Maybe is something else.
1732460620564.png
So assuming you have the new regulator on..and unit is turned off..

There is a test you can do which will prove to you that the generator is capable of making voltage and being stable. That will put your mind at rest that the issue is the regulator.

If you unhook F+ and F- from the regulator then carefully attach the wires you pull off to a 12 volt battery. F+ to positive, F- to negative...That removes the regulator from the circuit and pushes 12vdc down into the generator. Leave wires connected and restart engine...voltage should shoot up to around 220 VDC and be stable...Basically the battery is taking the place of the regulator and exciting the field in the generator to make voltage.
When I do this test I use wires with an inline fuse as the car battery I have for the 12volts has way too many amps for safety if the wires ground out by accident....really recommend you use fuse or circuit breaker on battery wires.
If that does not work, the problem is in the generator, if it does work you have now flashed the field at the same time as proving it functional.
Reconnect F+ and F- and set the voltage and frequency to 208V and 60Hz..

Just be super careful not to accidently short out the battery when attaching to generator wiring...just remember to push the 12 voltage into the gen, not into the regulator

Poccur
 