Good morning Guy,
All the more reason to get this genset under cover. Weather here this morning looks a bit ominous, but the investigation exercise shouldn’t take all that long. I’ll report back.
Guy,
No voltage at X,Y at K1, with Main SW in run position, battle short on, S5 Up, To ensure the contactor was in good shape, I removed it. Was a bit sticky, No sign of any water or rust, contacts needed dressing up. Coil measured 43 ohm. Ran out of daylight, will test coil / contactor with 24 VDC from battery in the Am. ( 24vdc applied across X,Y AT K1) 7-1/2 Control fuse appears to be a re-setable type, doesn't appear to be popped out (tripped) the other 2 fuses are good.
Any thoughts on next steps?