This is a non-generator related question.
I have a Square D QO load center. I'm in the process of adding a sub panel. Sub panel will be mounted ~3ft from the main panel. I'm aware that I need to remove the bonding screw in the sub to keep neutral/ground separate. I'll be running 4 gauge copper L1/L2/N and 10 gauge solid ground., feeding it with a 60A branch circuit from the main panel.
My main load center states that it can accommodate a MAXIMUM of 40 circuits. I'd like to add two tandem circuits in the main panel to create room for the sub panel.
QUESTION: Does a 240v circuit count as 1 circuit or two??? (in the context of the panel 40 circuit max)
Question 2: I've got my panel set up to properly back feed a 240v branch circuit. Does that count towards my 40 circuit limit??
Alternatively I know that I can extend to light/plug circuits and run those out of the sub panel. I believe there is an NEC rule that requires that any runs over 4' require an AFCI, which is no big deal other than I'm trying to keep costs down...
I can't find the exact model # of the panel on any labels on the inside. I believe this is the panel: https://www.royalwholesaleelectric....rcuits-200a-convertible-main-breaker-nema1-ul
I have a Square D QO load center. I'm in the process of adding a sub panel. Sub panel will be mounted ~3ft from the main panel. I'm aware that I need to remove the bonding screw in the sub to keep neutral/ground separate. I'll be running 4 gauge copper L1/L2/N and 10 gauge solid ground., feeding it with a 60A branch circuit from the main panel.
My main load center states that it can accommodate a MAXIMUM of 40 circuits. I'd like to add two tandem circuits in the main panel to create room for the sub panel.
QUESTION: Does a 240v circuit count as 1 circuit or two??? (in the context of the panel 40 circuit max)
Question 2: I've got my panel set up to properly back feed a 240v branch circuit. Does that count towards my 40 circuit limit??
Alternatively I know that I can extend to light/plug circuits and run those out of the sub panel. I believe there is an NEC rule that requires that any runs over 4' require an AFCI, which is no big deal other than I'm trying to keep costs down...
I can't find the exact model # of the panel on any labels on the inside. I believe this is the panel: https://www.royalwholesaleelectric....rcuits-200a-convertible-main-breaker-nema1-ul