What is wrong with an approved interlock device?I agree 100% that a doubled ended transfer switch is far safer.
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

What is wrong with an approved interlock device?I agree 100% that a doubled ended transfer switch is far safer.
Breaker load: NEC says 80% load continuous load, 100% Amps non-continuous load.You should definitely using a 60A breaker so that you have a safety margin. Whenever I figure a load I never max out a breaker 100% that just leads to problems and doing the same job twice. Rule of thumb I try to only use 90% capacity on the breaker. If conditions ever change you're going to have problems with an undersized breaker. Transfer switch is also proper I just installed one in my bosses house for his generator. It saves liability and other potential headaches.
By code a breaker can only be loaded to 80% of it's value. #6 awg copper is good for 60 amps, and you would have no issue only going 15-20' with it. Yes wire length does effect how much a conductor can carry. Roughly you have to up size every 100' as well as take in to account temperature the conductors.You should definitely using a 60A breaker so that you have a safety margin. Whenever I figure a load I never max out a breaker 100% that just leads to problems and doing the same job twice. Rule of thumb I try to only use 90% capacity on the breaker. If conditions ever change you're going to have problems with an undersized breaker. Transfer switch is also proper I just installed one in my bosses house for his generator. It saves liability and other potential headaches.
You should definitely using a 60A breaker so that you have a safety margin. Whenever I figure a load I never max out a breaker 100% that just leads to problems and doing the same job twice. Rule of thumb I try to only use 90% capacity on the breaker. If conditions ever change you're going to have problems with an undersized breaker. Transfer switch is also proper I just installed one in my bosses house for his generator. It saves liability and other potential headaches.
There are more potentially dangerous failure modes with an interlock setup versus a double ended transfer switch. I'm not at all condemning their use. I have a breaker interlock on my system. With that said if I was building a system from scratch it would absolutely have a transfer switch instead of an interlock setup.What is wrong with an approved interlock device?
I thought I saw an interlock on the bottom of the panel, so wouldn't that mean that the only way the generator breaker can engage (and therefore backfeed panel) is if the main panel breaker is disengaged? If main panel breaker is disengaged, the link between the utility and house is severed and OP is not really backfeeding power to the utility.You should never backfeed your panel linemen working on power outages could be hurt. A transfer switch the way to go.
This thread has turned into a debate about interlock versus transfer switch so I figured I would mention why I went the interlock route. For starters datadawg hit the nail on the head, as I did not want to pick select circuits as with most transfer switches and I am doubtful that most electricians would have connected a 20A generator through a transfer switch to a 250A service without forcing me to chose a handful of circuits. Plus I knew the current generator would not be the final one. If an 803 does what I need and becomes the final then I might see about buying an auto start board and having an auto transfer switch installed provided that I am able to power all loads except 50A and 60A ones. I was also considering a hybrid solar system with battery backup and figured that I would have it all rewired with auto transfer at that time. I am completely comfortable with the safety of the interlock and it was the best temporary solution. If money was no object and there was an actual safety concern I would have planned to call the electrician out 2-3 times until the setup was finalized.I agree a transfer switch is "better" and some modern units can give you nice features (like load shedding), but unless OP gets transfer switch that is entrance rated and can handle the entire panel load, he'll have to feed specific circuits through the transfer switch... a PITA.
Umm, a 50 amp breaker will trip at 50 amps, so what does it mean it can "handle a lot more than 50 amps"? If you are drawing say, 60 amps, a 50 amp breaker will trip to protect the wire from overheating and starting an electrical fire. Whether the breaker can "handle" 1,000 amps or 100 dancing elephants doesn't really come into play, it will simply trip at its rated capacity.Please also know that 6ga copper wire and a dual pole 50amp breaker can handle a lot more than 50 amps. As regarding breaker capacity, the breaker itself is overdesigned.
Not exactly. A 30 amp breaker will allow > 90A through it, for short periods of time. (That's how my heat pump that's has a 96A LRA can start and run on a 30A breaker.) The trip point of a breaker is some curve that takes current and time into account.Umm, a 50 amp breaker will trip at 50 amps, so what does it mean it can "handle a lot more than 50 amps"? If you are drawing say, 60 amps, a 50 amp breaker will trip to protect the wire from overheating and starting an electrical fire. Whether the breaker can "handle" 1,000 amps or 100 dancing elephants doesn't really come into play, it will simply trip at its rated capacity.
I know this is getting a little OT but it may be useful info.Not exactly. A 30 amp breaker will allow > 90A through it, for short periods of time. (That's how my heat pump that's has a 96A LRA can start and run on a 30A breaker.) The trip point of a breaker is some curve that takes current and time into account.