I have a 2008 DRASH unit, generator works perfectly but my issue lies with AC unit itself. Specifically getting the AC compressor to start and pump. If the soft starter starts the compressor, you can hear it run but it will not pump the refrigerant (verified by gauges).
However, I can manually press the contactor in on the soft starter with a screw driver and the compressor will start and pump.
anyone had this issue? I’m leaning towards a bad soft starter but not sure if something else would be tripping the thermal overload on the compressor. The soft starter itself is not tripping or throwing a fault code. Picture is of the soft starter I’m dealing with. Timers seem to be working as they should as it does delay when the call for cooling is on before it tries to start.
I have a 2008 DRASH unit, generator works perfectly but my issue lies with AC unit itself. Specifically getting the AC compressor to start and pump. If the soft starter starts the compressor, you can hear it run but it will not pump the refrigerant (verified by gauges).
However, I can manually press the contactor in on the soft starter with a screw driver and the compressor will start and pump.
anyone had this issue? I’m leaning towards a bad soft starter but not sure if something else would be tripping the thermal overload on the compressor. The soft starter itself is not tripping or throwing a fault code. Picture is of the soft starter I’m dealing with. Timers seem to be working as they should as it does delay when the call for cooling is on before it tries to start.