• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Dummy load?

WildernessJeep

Active member
187
89
28
Location
Huntsville, Texas
How are you guys putting a "dummy load" on your generators? I've got an 804 that is about ready to start running and testing, but I want to run it up to test the operation prior to plugging it in to something it might damage.
 

Scoobyshep

Well-known member
1,135
1,508
113
Location
Florida
I bought 3 elements for dryers (5500 watts each) and attached them to a blower fan. I can run a load of 72 amps at 240 volt with that

Sent from my SM-G950U using Tapatalk
 

Scoobyshep

Well-known member
1,135
1,508
113
Location
Florida
3 if you want a balanced full load. 2 can get a decent load but 1 leg will be higher

Sent from my SM-G950U using Tapatalk
 

Coug

Well-known member
Steel Soldiers Supporter
2,974
4,355
113
Location
Olympia/WA
Maybe keep your eyes peeled for a used 3ph A/C?
I bought one of the 3 ton Nordic Air ECUs. 3 phase heating coils are good for just under 10kw. I disabled 3 of the 9 heating elements, pulls 115% load on my MEP-802A 5kw.

The ECUs tend to go for really cheap at auction because they are all 3 phase and had the refrigerant drained. (recharging mine cost more than the unit did)
 

BobbyT

Member
65
37
18
Location
Little Rock, Arkansas
Another option that may be worth it if you just need a load bank once or twice, is to rent one. Most rental places have them or can get you one to rent from them. They are available in many different configurations and wattage capabilities.
 

cuad4u

Active member
268
88
28
Location
St Matthews, SC
I am an EE and have worked in electronics all my life. I used a 55 gallon plastic drum full of water. Clean water WILL NOT CONDUCT MUCH ELECTRICAL CURRENT - at not 240 VAC. I put my hand in the water while working to prove it to several people. I bought three 5500 watt water heater elements. I connected them in parallel for 16.5KW to test my 003A generators. You can add additional water heater elements for 30KW. Connect the elements to the generator and fire the generator up. If you want to load test the generator for a very long time, keep cool tap water flowing through the 55 gallon plastic drum. If you cannot locate a real dummy load this is the best next thing.
 

M35A2-AZ

Well-known member
Steel Soldiers Supporter
3,222
392
83
Location
Tonopah, AZ
I am an EE and have worked in electronics all my life. I used a 55 gallon plastic drum full of water. Clean water WILL NOT CONDUCT MUCH ELECTRICAL CURRENT - at not 240 VAC. I put my hand in the water while working to prove it to several people. I bought three 5500 watt water heater elements. I connected them in parallel for 16.5KW to test my 003A generators. You can add additional water heater elements for 30KW. Connect the elements to the generator and fire the generator up. If you want to load test the generator for a very long time, keep cool tap water flowing through the 55 gallon plastic drum. If you cannot locate a real dummy load this is the best next thing.
LOL, Great minds think alike, I was in electronics also.
 

98G

Former SSG
Steel Soldiers Supporter
6,066
4,429
113
Location
AZ/KS/MO/OK/NM/NE, varies by the day...
I am an EE and have worked in electronics all my life. I used a 55 gallon plastic drum full of water. Clean water WILL NOT CONDUCT MUCH ELECTRICAL CURRENT - at not 240 VAC. I put my hand in the water while working to prove it to several people. I bought three 5500 watt water heater elements. I connected them in parallel for 16.5KW to test my 003A generators. You can add additional water heater elements for 30KW. Connect the elements to the generator and fire the generator up. If you want to load test the generator for a very long time, keep cool tap water flowing through the 55 gallon plastic drum. If you cannot locate a real dummy load this is the best next thing.

Dump some salt in it and then stick your hand in....




I'M KIDDING ! DO NOT ATTEMPT! ! !
 

Scoobyshep

Well-known member
1,135
1,508
113
Location
Florida
I will "hold you're beer while you do this, and then explain to local authorities how it all happened..
best: mac/mc
You may laugh, but there were times at work that we were part of the circuit we were working on.

Sent from my SM-G950U using Tapatalk
 

mciikurzroot

Active member
Supporting Vendor
153
232
43
Location
wimberley texas
How are you guys putting a "dummy load" on your generators? I've got an 804 that is about ready to start running and testing, but I want to run it up to test the operation prior to plugging it in to something it might damage.
I have several actual real loadbanks that will handle the 804 series, if your set is portable i'd be pleased to share the time and effort to help you, i have all the cable combinations and can make it very easy to set up and prove out.
Alternate plan ?? for years i went with my home brew loadbank, using a package HVAC unit, removing the A coil and just using the heating elements and adding in additional heat strips to make multiple combinations to work up thru 18 kw 3 phase, the blower motor was always able to keep the elements very tame and i never lost a heat strip in any combination of testing efforts. It's only been in the past year suddenly it rained and 4 loadbanks came at me in differant packages and I moved away from my trusty homebrew model, i still have my home brew set up and you can have it free as well the assortment of heating elements including 416 volt strips total weight is 60-80 pounds and easily fit into a small size pick up .. so for a tank of gas it can be all yours.
Best: mac/mc
 

reset2

Active member
180
68
28
Location
Myersville MD
I use a used heat pump HVAC air handler. It works great. Most units have one two or three heating packs in them. Each pack is basicly 5kw each . The first run with my 802a worked great on the first bank but then I was so excited that a GovPlanet 802a was running and generating I forgot the second stage of heat started when the timer timed out and brought in the second pack (now 10kw). Never thought I moved so fast to shut it down. My 802 did not like 200 percent.
 
Top