Adding this to a very old thread. Cummins service bulletin for coil resistance.
https://quickserve.cummins.com/qs2/...service +doctype:26 +language: ( language:en)
Technical Service Bulletin Number Revision Level Date Group Number
TSB101553
QuickServe Online
Cummins Inc.
Technical Service Bulletin
Subject
Fuel Shutoff Valve Solenoid Resistance Specification
Original Topic Number: 05t5-3.
Warranty Statement
The information in this document has no effect on present warranty coverage or repair practices, nor does it authorize TRP or Campaign actions.
Contents
The purpose of this Service/Parts Topic is to notify the field of a change in electrical resistance specifications for the fuel shutoff valve solenoid. The new resistance specifications are more accurate than the old specifications. The new specifications are listed in the table below.
Revised Fuel System Shutoff Valve Solenoid Specifications
Voltage Resistance Minimum (Ohms) Resistance Maximum (Ohms)
6 VDC 1 5
12 VDC 6 15
24 VDC 24 50
32 VDC 42 80
36 VDC 46 87
48 VDC 92 145
74 VDC 315 375
115 VAC 645 735
In all cases the solenoid terminals must be thoroughly cleaned before the measurement is taken. In the case of the single pole solenoids, it is recommended to scrape paint off another portion of the solenoid cast iron housing. Good contact pressure with the multimeter terminals is recommended as well as a stable measurement on the display before the reading is compared against the specifications.
Procedure 005-043 (Fuel Shutoff Valve) is being updated to reflect the new specifications.
Related Procedures
09-005-043 Fuel Shutoff Valve
Last Modified: 14-Dec-2004
Feedback / Help
Copyright © 2000-2010 Cummins Inc. All rights reserved.