Keith_J
- 1,325
- 113
- Schertz TX
If the generator is under 5kW and connected by plugs only, no grounding is needed per NEC. If this is used in the Texas Hill Country, grounding might be impossible as soil depth is often nil and limestone solid.
The MEP-016s have exposed load terminals...I will probably build a genset-mounted panel for NEMA 5-15/20 and cover up those exposed terminals because despite Boy Scouts being above average in smarts, the council might not like it. And the underwriter will have a problem.
Yes, you CAN use galvanized pipe for grounding! And insulated THHN/THN wire for grounding. If needed, I can cut a nice spike on a section of 1" galvanized pipe and hammer the end into a spike, welding the seam. Heavy but effective.
Just returned from the initial meeting with the OP. The generator looks rough but the engine is nearly new. Aside from cosmetics, it is fully functional, starting in 50F weather on the first pull. Voltage and frequency meters are spot on at both load terminals and convenience outlets.
Discussed safety issues and planned to make a L5-30 receptacle mounted to the generator on a panel covering the load terminals for safety. Might be two receptacles, depending on the SOW wire the OP has available and the distance. Also will make a distribution box for the end of the SOW for standard NEMA 5-15 or 20 duplex receptacles. This box will have 20 amp breakers for each receptacle.
With this modification, no grounding is necessary although GFCI receptacles would offer additional safety.
Because a cold front blew in last night, we were getting quite chilled. We have a plan and a working generator. And I have an entry back into Scouting.
Here is a good source for two NEMA 5-20R duplex, breakers and a L14-30R, all for about $9. http://www.surpluscenter.com/item.asp?item=11-3306&catname=electric
The wiring is substandard but the receptacles and breakers should be fine.