Grounding Mep-802a while load testing etc

ribs1

New member
29
21
3
Location
Michigan
Hello,
I have the Map-802a properly grounded when connected to my house through a transfer switch.
My question is when I am not connected to the house for load testing or other purposes do I need to reattach the ground strap and drive a ground rod?
Thanks
 

Mullaney

Well-known member
Steel Soldiers Supporter
Supporting Vendor
7,771
19,879
113
Location
Charlotte NC
Hello,
I have the Map-802a properly grounded when connected to my house through a transfer switch.
My question is when I am not connected to the house for load testing or other purposes do I need to reattach the ground strap and drive a ground rod?
Thanks
.
Like @DieselAddict said, ground it.

The reasoning is pure simple safety and logic.

There really aren't but two choices:
1. Drive (and test) the ground
2. As the human, YOU can be the ground (bad for your health)

Humans being mostly water and maybe on damp grass or dirt conduct electricity really well.
Your personal goal naturally is to stay alive and not be the conductor.
.
 

Attachments

Elijah95

Certified Rookie
1,239
1,201
113
Location
Georgia
Hello,
I have the Map-802a properly grounded when connected to my house through a transfer switch.
My question is when I am not connected to the house for load testing or other purposes do I need to reattach the ground strap and drive a ground rod?
Thanks
I’m generally lazy, but after being bit by an un-grounded set, I now go ground crazy. Cheap insurance.

Ps the shock doesn’t give you superpowers sadly


Sent from my iPhone using Tapatalk
 

nextalcupfan

Well-known member
348
507
93
Location
NW Missouri
When I was doing initial testing after I first got my 803a I did ground it, though probably not enough.
I drive a piece of rebar into the ground about 6-8in and hose clamped some wire to it.

I DID have continuity to the ground from the set though.
 

ribs1

New member
29
21
3
Location
Michigan
I have a reliance pro/tran transfer switch. Can I just plug the generator into the power inlet box but not switch the transfer switch from line to gen? I am pretty sure the ground goes all the way through and is not switched?
I did have an electrician install this switch.
Thanks
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,541
2,090
113
Location
Efland, NC
I have a reliance pro/tran transfer switch. Can I just plug the generator into the power inlet box but not switch the transfer switch from line to gen? I am pretty sure the ground goes all the way through and is not switched?
I did have an electrician install this switch.
Thanks
You are correct that the ground should not be switched. Making that connection would ground it.

I don't know if you run your generator in the same place all the time but just as a FYI, I have a ground rod driven where I work on generators that I use to ground them. Ground rods are pretty cheap and assuming you don't have rocky soil (like I have here) they are not too hard to sink. Well worth the safety factor.
 