Help with MEP-004a Day tank not filling

carlton

New member
4
0
1
Location
United States
there are 2 lift pumps which fill the day tank which gravity feeds the motor/injector pump. these 2 pumps are not powering on to fill the day tank. iIf i mnually fill day tank genset runs until day tank is exhausted. float switch seems to function at both low and high levels trying to figure out where to start trouble shooting or if i should just hardwire the pumps. Thank you in advance
 

Guyfang

Moderator
Staff member
Moderator
16,758
24,064
113
Location
Burgkunstadt, Germany
First, make sure the 3 way fuel valve is turned to set position.
Then place the S2 in the run position.
Place the S7 in the up position.
Do the pumps come on?
If not, unplug the fuel pumps. Take a wire and run it from the + terminal of the starter, to the plug on each pump. Do they both come on?
 

jmenende

Well-known member
467
389
63
Location
Puerto Rico
Place s2 (start switch) in the run (middle position) amd flip the red battle short switch. That will turn on the pump. Let it run till the sound changes. System should be primed. If you dont hear the pumps check for 24v and pump power inlet. Also, unscrew the bottom pump lid and make sure the filter is clean. While your at it, stick your pinkie in thr bottom and make sure the pump piston moves. If stuck use carb cleaner to break loose. Good luck.
 