2Pbfeet
- 1,326
- 93
- Mt. Hamilton, CA
There's always some new paint...
Congratulations on the new to you generator.
All the best,
2Pbfeet
All the best,
2Pbfeet
Did some testing today, I figured I would add on to this, just for anyone finding this thread from GoogleNotes from running on the Light Tower Marathon 6Kw pancake plugged into the 240v/30a twist lock:
7/8 at 5:30am started powering the whole house, 5198 hours. 4 ton AC unit started and ran fine. Added the neighbor's two refrigerators. The florescent and LED lights would flicker. The microwave just did not heat items as fast. Kept all electronics off.
With the AC running and all the little draws would pull 19-20 amps per leg. The little Kubota would barely change tone with the change in load, every impressed.
7/9 9am shut the Light Tower down to switch to the MEP802. Run time at this point was 31 hours. The crude fuel usage came to ~12 gallons or ~.4 gallons/hour. Really love the 30-gal onboard tank!!!
7/10 Ran heavy power cord from the light tower to the neighbor's panel. Would not start their small AC unit and would trip the 20 amp breaker on the LT. They do not have any Hard Start/Easy Start installed. Ran all their lights, fans, and refrigerators. Easy pulled 10 amp per leg.
7/11 Power was restored, 5265 hours, total run time 67 hours. THANKS TO ALL THE LINEMEN THAT CAME TO OUR NEED AFTER THE STORM HAD PASSED!!!!!!
Post storm review: Pros
The Kubota D1005/Marathon Pancake 6kw generator did not faulter at all even at 19-21 amps per leg.
Very impressed with the fuel usage at ~.4 gallons/hour. MEP802 ~.72 gallons/hour.
Cons: need to "Clean" the power output to maintain 60 Hz and 240 vac. Has anyone in the Forum installed an AVR, line filter, or other devices to "CLEAN" the output?????
I think that it rarely hurts to replace an old capacitor like that, especially in a unit of unknown history, and always good to keep a spare on hand. If it were me, I would test load it after changing to make sure everything works. Capacitors aren't the most reliable parts in the box in my experience.It will be interesting if I have enough base load in my house that I don't need the resistive heater, I will probably try a few more items on their own first before plugging into the house and giving it a go
Going to pre-emptivly replace the capacitor since its old, hopefully I got the right one!
GENTEQ 97F9632 - 25UF, 440V, 6%
I'm not an electrical engineer, but I can see how a bad cap would be doubly as bad for these gensets in that caseFWIW: If there is not enough load on a capacitor regulated generator, the rotor often doesn't set up enough of a field and the voltage level can sink by a lot as the next bit of load comes on line, causing modern electronics to either drop out completely (like UPS units) or perform poorly for a bit until the voltage comes back up.
I find that an issue / challenge with UPS units is that when they have tight limits on acceptable input voltage/frequency, the droop upon loading can cause the UPS to decide the voltage / frequency is out of range, and drop off line, as @Toolslinger posted above. Then you have a rinse and repeat cycle going. Some, but by no means all, UPS units can be programmed/adjusted to accommodate a wider variation in input voltage and frequency. A few of the brand name units (e.g. Eaton) require the use of their program, or app, to set the allowed values to something non-standard. The flip side and good news is that they can be adjusted to have different values.I'm not an electrical engineer, but I can see how a bad cap would be doubly as bad for these gensets in that case
It will be interesting to test the house, I have a double conversion UPS that powers all my network, computers, TV, etc. The load rarely dips below 900w, so that's a good constant load
If that load would serve in place of the heat gun, then I pretty much never have to worry!