Thanks, this seems to be a 5 minute job then.

This will enable me to run more that one machine at a time as the 440>220 setups prevented this.

Thanks again!!
Make sure to double check the Fuse Ratings, to make sure your electrician left the fuses for 220V configuration in place as you believe he did.
 

Rik

Member
58
53
18
Location
California
Make sure to double check the Fuse Ratings, to make sure your electrician left the fuses for 220V configuration in place as you believe he did.
I checked them when I was originally just trying the wiring by changing the lead arrangement on the head motor.

Thanks!
 

peapvp

Well-known member
Steel Soldiers Supporter
1,258
1,592
113
Location
Basehor, KS
Just to clarify, L1 to L3 and L2 to L4 but no connector between the two?
Interesting, don’t apply power to the configuration in your pictures

you need to make 2 jumpers for each transformer
One jumper connects H2 and H4 together - connect L2 to H4

the other jumper connects H1 and H3
Together - connect L1 to H1

IMG_4246.jpeg
 

Rik

Member
58
53
18
Location
California
With the 440v setup, L1 went to H1, and L2 went to H4 while H3 & H2 were tab'd together.

Reading what you are saying, is that through the jumper, won't H1, H2, H3 & H4 all be connected together?

So I attach the tab back between H2 & H3 and then jump H4 & H1 into (H2,H3)?

Thanks!
 

peapvp

Well-known member
Steel Soldiers Supporter
1,258
1,592
113
Location
Basehor, KS
With the 440v setup, L1 went to H1, and L2 went to H4 while H3 & H2 were tab'd together.

Reading what you are saying, is that through the jumper, won't H1, H2, H3 & H4 all be connected together?

So I attach the tab back between H2 & H3 and then jump H4 & H1 into (H2,H3)?

Thanks!
No, you have to exactly do it the way I showed it in post #46
If you do not understand this or this is beyond your comprehension and capabilities, then you need to retain a licensed electrician.

Everything you stated is full blown short between two phases.
This tells me that you do not understand the fundamentals involved and you should NOT proceed on your own, but hire a professional before you electrocute yourself to death.
I do not attend funerals. Thank you
 

Rik

Member
58
53
18
Location
California
No, you have to exactly do it the way I showed it in post #46
If you do not understand this or this is beyond your comprehension and capabilities, then you need to retain a licensed electrician.

Everything you stated is full blown short between two phases.
This tells me that you do not understand the fundamentals involved and you should NOT proceed on your own, but hire a professional before you electrocute yourself to death.
I do not attend funerals. Thank you
I understand what you are saying, but with the link between H2 & H3, as shown in the photo, this is effectively the same thing. Unless I remove the link between H2&H3…
 

peapvp

Well-known member
Steel Soldiers Supporter
1,258
1,592
113
Location
Basehor, KS
The wiring diagram does not show a jumper between H2 and H3, this is self explanatory and this implies, by using common sense, that any currently installed jumper between H2 and H3 has to be REMOVED.
 
Last edited by a moderator:

Triple Jim

Well-known member
1,393
334
83
Location
North Carolina
I all fairness, that table is very confusing. The first line says that for 480 you connect H2 and H3, and signifies this with a hyphen between them. The second line for 240 then puts a hyphen between H1H3 and H2H4, seeming to say to connect those pairs together!

Instead it should have:

H1-H3; H2-H4

The simple answer is to connect the two windings in series for 480 and in parallel for 240.
 
  • Like
Reactions: Rik

Rik

Member
58
53
18
Location
California
The wiring diagram does not show a jumper between H2 and H3, this is self explanatory and this implies, by using common sense, that any currently installed jumper between H2 and H3 has to be REMOVED.
Ok, I didn’t add the jumper and I don’t see any “jumper wire” in the cabinet from when the machine was originally wired 220v an removed to convert to 440v
 