• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Libby 802 Coolant temp.

PoP PoP

Member
45
0
6
Location
Cerro Gordo NC
Libby Mep 802. I am still in the testing phase for my unit. Today I hooked up a new heater as recommended here by some( Comfort Zone CZ220 Ceiling-Mounted 3-Setting Fan-Forced Industrial Heater) 3.5k, 4k and 5k settings. In the 5k setting I was pulling 20 amps at 240 volts. Calculations say 4.8 k . I did see a rich, dark looking exhaust. Maybe a bit more rich than expected. I also noticed the temp steady at 160 F. I then measured with a laser probe temp sensor, it showed 160 also. After looking through the TM and several post here I think I have a 160 thermostat in there. I think and guess that I need to replace it with the 180 F thermostat MU55358, gasket 2138. Also note the exhaust muffler was 320F if I remember. The engine body temp was 160 F also. I am NOT a mechanic but think it would possibly help with some wet stacking if those conditions exist for me later. I was also thinking the engine would perform better/ more efficient/more horsepower. I would like some opinions on whether to replace it or leave it. I am in N. Carolina where it is pretty hot. My end goal is to have a whole house setup with manual load management. My needs are 4 ton heat pump (emergency elements off), 2 refrigerators and 1 freezer. Miscellaneous lights and TV. Stove microwave and water heater managed with out the ac on of course. I do have a cloths dryer but I can live with out it for a long while so it is not even considered. No water pump to consider as well. I will plan to get an 803 and keep the 802 as a back up. Big question for me is do I need an 803. The cost of the generator is not in the calculation ( I am not rich but $3 or $4 k is not going to make difference in my decision). Our issue here for the past several years is hurricanes leaving us with out power for a week or so twice. I need and desire AC. Thoughts on this sizing also.


 

Coug

Well-known member
Steel Soldiers Supporter
2,975
4,356
113
Location
Olympia/WA
Without knowing the exact specs of the heat pump it's kind of hard to give an exact answer, but most likely you'll need the 803 as a run of the mill 4 ton heat pump is going to be minimum 26 amps and max of 40-45 amps surge on 208/240VAC. The two freezers, fridge, lights and TV are almost negligible in comparison, depending on specs for them you might be anywhere from a half KW when everything is running up to a couple KW if everything cycled at the same time. Microwave you can count on another KW, the stove depends on what part you are using, anywhere from 1kw up to 4 or 5kw with oven on, and the water heater if it's electric is also in the 4.5KW range give or take a KW.

I usually deal with explaining Generac standbys to customers, and as they're primarily natural gas or LP they don't care about being run on light load, whereas these military gens thrive under heavy load but don't like light loads.

The 802 would handle everything except for the heat pump with load management, it's what I do at my own house (I'm fortunate enough not to need aircon where I'm at), but adding in the heat pump personally I'd say go for the 803 instead, I seriously doubt you'll be unhappy if you do, but the 802, while it might be barely enough to handle what you're talking about, probably isn't quite enough to do so with any comfort margin.

As for the 160 thermostat, in the manual it says the thermostat is supposed to start opening at 160, and be fully opened at 185, so I'd say most likely it needs replaced with the correct one.

It also says normal operating temp is 170-200, and since you checked the actual temps on it and not just relying on the gauge, I'd say replacing it's a good idea.
 

Bmxenbrett

Member
602
30
18
Location
NY
An 802 can run a few window units that you keep in your basement for alot cheaper than buying and maintenance on two generators.

We need more specs on your AC.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,841
5,954
113
Location
MA
You owe it to yourself to do an amp load calculation on your 'must run' items, to determine a baseline. All the machines should have data plates/stickers on them which show how much power they actually use. Tally that up and let us know. Then you move down the line from 'needs' to 'wants'.
 

PoP PoP

Member
45
0
6
Location
Cerro Gordo NC
I have done the numbers and as long as they do not start up at the same time it squeezes in. Barely. How about the thermostat question? Libby Mep 802. I am still in the testing phase for my unit. Today I hooked up a new heater as recommended here by some( Comfort Zone CZ220 Ceiling-Mounted 3-Setting Fan-Forced Industrial Heater) 3.5k, 4k and 5k settings. In the 5k setting I was pulling 20 amps at 240 volts. Calculations say 4.8 k . I did see a rich, dark looking exhaust. Maybe a bit more rich than expected. I also noticed the temp steady at 160 F. I then measured with a laser probe temp sensor, it showed 160 also. After looking through the TM and several post here I think I have a 160 thermostat in there. I think and guess that I need to replace it with the 180 F thermostatMU55358, gasket 2138. Also note the exhaust muffler was 320F if I remember. The engine body temp was 160 F also. I am NOT a mechanic but think it would possibly help with some wet stacking if those conditions exist for me later. I was also thinking the engine would perform better/ more efficient/more horsepower. I would like some opinions on whether to replace it or leave it. I am in N. Carolina where it is pretty hot.
 
Last edited:

Coug

Well-known member
Steel Soldiers Supporter
2,975
4,356
113
Location
Olympia/WA
160 is too cold. You've verified that it's staying at that temp using the laser probe temp sensor and not just a gauge error.

The TM says it should be 170-200 during normal operation, if it's below that under a load, then something isn't right, so get a new thermostat and gasket installed and check to make sure that takes care of it. I'm not as familiar on these as some, but I don't see what else it could be other than the thermostat is the wrong one, is opening early, or maybe has something preventing it from closing.
 

Guyfang

Moderator
Staff member
Moderator
16,784
24,129
113
Location
Burgkunstadt, Germany
The thermostat and gasket are cheap. Drain the coolest into a clean container. Reuse if clean. One way or another, you are going to have to look at it, as it's running too cold. Running at the right temp means less wet stacking. What's to contemplate here? One step at a time. Fix the small problems, the big ones go away.
 

pjwest03

Active member
278
37
28
Location
Vestal/NY
The thermostat itself is an easy job. Not too hard to access. The real PITA is re-filling with the horizontal radiator cap. There are some really nice plastic funnel kits on E-Pay and Amazon that connect to the filler neck and make for much reduced swearing.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,841
5,954
113
Location
MA
And more of a PITA if you have a trailered set. At least with the genset only, you can put a block under the radiator fill side to tilt the machine to help.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,841
5,954
113
Location
MA
And to the OP, have you had this machine fully loaded for testing purposes? The dark smoke could very well be due to top end wet stacking that is burning off... or it could be something else. Let us know more about how you have seen this machine run before (or if you havent). Won't hurt to throw a full bottle of Seafoam into the tank while you do this, to help clean things up. Hows your oil pressure? Do you have any noticeable blowby?
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,841
5,954
113
Location
MA
For certain if there is a will, there is a way. Not everyone has the same fun toys though ;)
 

PoP PoP

Member
45
0
6
Location
Cerro Gordo NC
And to the OP, have you had this machine fully loaded for testing purposes? The dark smoke could very well be due to top end wet stacking that is burning off... or it could be something else. Let us know more about how you have seen this machine run before (or if you havent). Won't hurt to throw a full bottle of Seafoam into the tank while you do this, to help clean things up. Hows your oil pressure? Do you have any noticeable blowby?
My response is back to about five of you. I had read the TM and other threads. I did replace it yesterday. I had to use the old part number to get a substitute FYI. As stated it was easy. It came up to temp 180 and ran well. I put 4.8 k resistive load for 20 minutes and I felt like the light in volume dark smoke cleared up to the point that you had to almost look for it. It is definitely not chugging smoke. Blow by.... I pulled the dip stick while running and it seemed to be under vacuum for 1/2 second then have a small positive pressure. Will check again when I finish these fuel lines. Oil pressure is real good at 50 or 55. Not much run time on it because I have been trying to buy an 803. Originally this was to be a parts machine but it has been somewhat easy to bring back. Misc. stuff like no alt. which I got from LIGHT IN THE DARK and many cut wires. I then found the very small pin hole in the fuel line. I panicked for a bit till I found the easy fuel line fix post As Guyfang has said a picture is worth thousands of words. I thought I was going to have to buy the $165 metal tubing. The crimp was a bit tough to get off but it was not so bad. The other one looks to be a bit more harder to get to. Anyway I will get it done. I kinda fell in love with the 802 is the reason I was wanting it to be my home gen. Plans for now is to continue with the 802 for the primary connection and I will continue to the search for an 803. I have bid on many here in NC. Just keep coming up short. I can afford to pay for a good one but more than $2.5k for a pig in the sack does not make sense to me. I had rather pay $3.5 for a tested running machine. When I do acquire the 803 I can just swap it out and have the 802 as a minimum get by back up. Plan to do a real nice clean legal setup. For now I will watch the smoke and performance and report back at a later date if the thermostat made a really big difference. Hate it when the later feed back is not posted, so others can learn from our efforts. I do read the old post for solutions and the the TM. I have the ultimate well nuts. But I do not have a leak and they feel pretty tight. Yet another decision to make. The tank is full and may change it out when empty. Not that I am lazy just hate to "fix" something that could outlast me as is and knowing it will be the back up plan. Ok maybe I am lazy. Thank you for the replies and follow up questions.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,841
5,954
113
Location
MA
Well if it cleared up to a very light haze, I'd say you are doing pretty good (seeing as there is no emissions equipment on these). The key with the 803s... patience. Good luck!
 

Bmxenbrett

Member
602
30
18
Location
NY
If you ever have the top cover off do all the return lines and well nuts. Its alot easier to do both of these with the cover off.

May be worth having 2 well nuts and a roll of return line laying around. Its prob $65 in parts.
 

PoP PoP

Member
45
0
6
Location
Cerro Gordo NC
I am doing those today and tomorrow. Just replaced the high priced braided lines at the filter. Had them made up this morning.
If you ever have the top cover off do all the return lines and well nuts. Its alot easier to do both of these with the cover off.

May be worth having 2 well nuts and a roll of return line laying around. Its prob $65 in parts.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks