Today we had the opportunity to play a little with some power, have a 125KW genny that had an IP replaced and 'needed' to load test it to verify the repair, *not really but its fun*
Largest load tester I have is Essex A698,

We ran the load tester wide open, pulled 225 amps per leg, guessing about 75kw, you could feel the cable humming.

Ran the genny about 10 minutes full load on tester and we 'smelled' something warm. A couple of the loads were letting off some smoke, amp values did not change enough to notice
*video is loud, turn down your sound*
youtube.com
So, I guess my question is, are these supposed to smoke? I did not have this issue with 33kw, I did use compressed air and blew off all the dust prior to running, nothing else was hot except the load cells, had 1ea 1.25 cell that smoked and 2ea of the 2.5 cells that smoked,
any suggestions or comments or complaints are greatly appreciated.
Largest load tester I have is Essex A698,

We ran the load tester wide open, pulled 225 amps per leg, guessing about 75kw, you could feel the cable humming.


Ran the genny about 10 minutes full load on tester and we 'smelled' something warm. A couple of the loads were letting off some smoke, amp values did not change enough to notice
*video is loud, turn down your sound*
- YouTube
Enjoy the videos and music you love, upload original content, and share it all with friends, family, and the world on YouTube.
So, I guess my question is, are these supposed to smoke? I did not have this issue with 33kw, I did use compressed air and blew off all the dust prior to running, nothing else was hot except the load cells, had 1ea 1.25 cell that smoked and 2ea of the 2.5 cells that smoked,
any suggestions or comments or complaints are greatly appreciated.