Guys, just a quick question. When performing the manual flash on my genset( when I fisrt got it running) I noticed the starter tried to engage. It made a very unhappy sound and I stopped.:confused: I thought it was not supposed to run when this was done. Any suggestions?? Thanks
Jim
 

Speddmon

Blind squirrel rehabiltator
Super Moderator
Steel Soldiers Supporter
4,640
28
38
Location
Cambridge, Ohio
There is a start disconnect switch located just above the oil filter canister toward the rear of the engine. It looks like a funky oval shaped cover with a wing nut holding it on. If your started tried to engage after the set was running that's probably your culprit. I don't have the number right off the top of my head, but that switch is supposed to open at around 900 RPM's I believe.

On a side note, you should not have to manually flash the field except for rare occasions, as any residual magnetism in the iron of the gen head should be enough to get it to start to produce power. That switch can be cleaned and adjusted, but it's a pain in the butt. Another member here did it, and has some details about it, I'll see if I can find it.
 

DieselBob

Active member
2,891
13
38
Location
Arnold Maryland
There is a diagram of the "Start Control assembly" in TM5-6115-585-24P, Page 136 Figure 43. Haven't had one open so not much help.

You might check and see if some enterprising individual bypassed the assembly.
 
Last edited:

Diamondjim11

New member
54
0
0
Location
Sunbury,Pa
Since the set showed no voltage output at first following the tech man and advice from the guys I thought I would try it. After the set was running, I turned the start switch from run back to start. It made a loud grind as the starter tried to re-engage the flywheel. Perhaps I did not have it running fast enough. Is there a minimum speed it should be at before trying? Remember at this time I still had nothing showing and engine speed perhaps was not high enough yet.
Jim
 

jbk

Member
404
5
16
Location
livingston la.
i believe its 650 rpm . you can try cleaning the contacts first. get a can of contact cleaner spray the contacts liberally and pass a piece of paper between the contacts a few times. i would try this before adjusting them unless their bent or way out.
 

Speddmon

Blind squirrel rehabiltator
Super Moderator
Steel Soldiers Supporter
4,640
28
38
Location
Cambridge, Ohio
i believe its 650 rpm . you can try cleaning the contacts first. get a can of contact cleaner spray the contacts liberally and pass a piece of paper between the contacts a few times. i would try this before adjusting them unless their bent or way out.

That's good advice, but one step above the piece of paper would be to use a greenback (a plain old dollar bill) The bills are a cotten fiber and not paper and are just abrasive enough to clean the contacts without removing material like sandpaper will
 

Crash_AF

Active member
1,530
7
38
Location
Colorado Springs, CO
Yea, that's the correct way to flash the field. I just wanted to make sure you weren't jumping wires or anything... LOL You'd be surprised what I've seen people try to do without reading the TM.

It does sound like the starter disconnect/lockout switch isn't adjusted right or is completely inop. Follow Speddmon's advice and check it out. Test & adjustment procedures are in the -12 TM Section 4-28.

Later,
Joe
 