MEP 002A and 003A

a109836

New member
8
0
0
Location
Cache, OK
Does anyone know the part number for the connector from fuel tank to aux fuel pump for the mep002a. My generator just has two wires where it is suppose to be plugged into the tank float.
 

BobbyT

Member
65
37
18
Location
Little Rock, Arkansas
Mine shows MS3057-4B BENDIX 8022 on the collar the wire goes into, then the body of the 90 says ITT CANNON 10 SL.
Not sure where to get it, but searching online for MS3057-4B showed lots of places listing it.
Connector.jpg
 

Jkid3

New member
4
0
0
Location
Clinchco Va
I Am new here. I have a question about my MEP-002A. I have been told it is hard on voltage regulator to idol for a long period of time. I want to know if it is hard voltage regulator to idol and warm up and charge the batteries?

Thanks
 

Dock Rocker

Active member
980
72
28
Location
Jackson ms
I mean to idol and warm up and charge the batteries with no load on generator.

Thanks
Not sure if this is the correct place for your question I would put it in the Auxiliary Equipment forum if you want a real answer.

I don’t think you are supposed to idle these sets at all. I think they are supposed to run at operating RPM all the time.


Sent from my iPhone using Tapatalk
 

Guyfang

Moderator
Staff member
Moderator
16,777
24,103
113
Location
Burgkunstadt, Germany
If you want to do something good for your gen set, star it up, run it at 60 hertz and hook up some kind of load to it. The more, the better. Run it a few hours. Do that, and you gen set will love you.
 

Keith_J

Well-known member
3,657
1,323
113
Location
Schertz TX
Generators work by spinning a magnet inside a coil(s). These generators use an electromagnet and the electricity for this magnet comes from the voltage regulator. So running a set at lower than rated speed causes the regulator to max out. This burns the output transistor.

Yes, I simplified the operation by skipping over the exciter section and rotating rectifiers...along with CVT and other magic.
 

BlackhawkMTP

Member
43
8
8
Location
KY
Is there anyway to reference the articles linked in Post #1 of this thread again? When I click on the links it seems like the website has deleted the thread due to old content or something. I believe this is very good information contained in here as I have recently bought 2 MEP-002a generators that I am trying to get back in service. Any help would be appreciated! Thanks fellas.
 

Gypsyman

Well-known member
Steel Soldiers Supporter
333
741
93
Location
Quincy, FL
Here you go. Link corrected.

 
Last edited:

derf

Member
926
13
18
Location
LA
Also, maybe

 
Top