I have an 002 hooked up to the house. I decided this morning to start it up and run it for an hour or so (it's been about 3 months since the last test). It has been connected for over a year and I have never had the following issue when testing it.
All seems to be fine. I was running it at 20-25%. I decided to put a bigger load on it. First I started the dryer (it ran it before at 105%) with the rest of the basic load. I have a Kill-a-watt meter in the house. HZ dropped from 61.5 to 60.5 but the voltage dropped to 85 volts (in the house but at the generator it was still on 240). I shut the dryer off and then tried the deep well pump. Basically the same result, HZ was good but the voltage dropped.
Is it maybe because there was an unbalanced load on the one leg?
Any other ideas?
Thanks
ETA: The generator didn't seem to mind the load. There was barely a grunt when starting the dryer or pump.
All seems to be fine. I was running it at 20-25%. I decided to put a bigger load on it. First I started the dryer (it ran it before at 105%) with the rest of the basic load. I have a Kill-a-watt meter in the house. HZ dropped from 61.5 to 60.5 but the voltage dropped to 85 volts (in the house but at the generator it was still on 240). I shut the dryer off and then tried the deep well pump. Basically the same result, HZ was good but the voltage dropped.