I accicentally won two lots of 2 -002a's on a M103 trailer out of DE last week. Loaded them up and got them home no problem the hours were 351, 451 on one trailer and 351, 1 on the other with the latter trailer having better looking generators. All of the units had Mfd dates of 1982/3 and all fluids were flushed on the units and the fuel lines to the tank disconnected.
I started with my two good units namely the 1 hour one first. I believe that this one is a true one hour unit as there is no overhaul tag on this (or any unit) and the problem I found was that the governor shock type linkage's plastic ball joint clip had split and would slide when pulled. I put a hose clamp on it to lock the plastic on and it has not been a problem since. I have load tested it to 5kw for a half hour and there appears to be an issue with the breaker.
1)After running for 15 minutes the breaker drops out and opens up so I reset it and it will run another 15 minutes and repeat the same issue. Has me stumped but this one is not my priority at the moment.
Unit #2 with 351 hours just needed fluids and runs like a top with no issues in a hour load test at 5kw.
Unit #3 with 451 hours was found with a stuck IP and a broken bowtie clip in the IP. I took it all apart and rebuilt if after getting parts from AMBAC ( call them the nice lady took more than 1/2 off the price compared to their online catalog and it was a A+ experience). So I put the IP back in and time it 180 deg out, curse a bit and then reinstall it with the correct timing and it starts right up and runs like a top. On a side note the fuel tank had built up crud as well as the fuel system so the tank was cleaned and the usual system flush and filter exchange. The fuel line on both units #3 & #4 from the check valve to the IP were shot and basically was just the spring to I made up a new one from soft copper and flared the ends.
Now onto the real problems for #3, the unit does not make power. I spent all weekend working on the unit tracing everything, manually flashing fields and trouble shooting the unit with some success and some failure and here is what I found. Right off the bat the speed switch was off as it pulled the starter in constantly so that was fixed in order to manually flash the field. Once running the manual field flash going back to start did nothing so I started to look at why and tried applying 12V to TB5-6? iirc, its listed in the tm, and had no success. Went onto looing at the diodes and I found that one diode had the solder joint fail, reattached it and retried the 12V to the point. SUCCESS, we were making power as long as I had 12V energizing that connection for the field. As I kept digging, I found that the rectifier bridge A4 was giving me a problem on for the field flashing and when I would ring it out it was ringing on almost every terminal which I verified in the good unit that it should not be. Took the board off and low and behold a solder bridge failed and melted, installed new jumper wires and verified that the components to what I believe are ok and put it back in the unit. I know the voltage regulator is fine since I took it out and put it in my running unit and had zero issues. Now I go to start the thing and the + line from my slave cable that is loose decided it wanted to go to ground so it wiped out my DC side. My real question is that the unit will try to start and will run but the fuel pumps will not. The glow plug relays pull in, dash lights work, start solenoid all work but the fuel pumps do not come on line I will mention that the DC breaker on the dash did not trip and is operating as normal. I disconnected the power supply to the fuel pumps and rung the wire out and am finding that it goes to ground before going to the pump. Any one have any ideas where to look before I ring every wire out?
2) DC circuit is shorting out before powering the pumps but the unit will try to start it just is not getting fuel. The unit also when it ran after being shorted, had the voltage meter indicating overcharging at one time and ran normal the other time with the fuel pumps working.
Unit #4 had the same IP issue so it was removed and rebuilt but when it was put back in it would not start up. I was getting fuel up to the injectors but it does not look like the fuel was going through the injectors into the engine. To me it looks like the injectors either were to popping or the pump was not developing enough pressure. I had all of the injectors apart on the two units and cleaned them up with the exception of the actual spring in the injector as I cannot figure out how to get it apart the cap comes off but does not bring the body with it to get down to the springs. I wonder if crud and algea got into the injectors.
3) injectors will not pop, either the pump is not making full pressure or the injectors are gummed at the springs
On a side note, units #3 and #4 o the fuel side were terrible!! Algea had taken over and I had deposits everywhere in the fuel system. Brake cleaner was needed to clean the IP's and get the parts to even move. Both of the on/off slides in the IP were seized due to being gummed up and luckily did not break any other components other than the bow tie. If you have diesel that sits, make sure you treat it. I always treat my fuel for bacteria as well as lubrication with this ULSD being rougher on older equipment but lets not talk about that debate.
Any help on these questions would be wonderful
I started with my two good units namely the 1 hour one first. I believe that this one is a true one hour unit as there is no overhaul tag on this (or any unit) and the problem I found was that the governor shock type linkage's plastic ball joint clip had split and would slide when pulled. I put a hose clamp on it to lock the plastic on and it has not been a problem since. I have load tested it to 5kw for a half hour and there appears to be an issue with the breaker.
1)After running for 15 minutes the breaker drops out and opens up so I reset it and it will run another 15 minutes and repeat the same issue. Has me stumped but this one is not my priority at the moment.
Unit #2 with 351 hours just needed fluids and runs like a top with no issues in a hour load test at 5kw.
Unit #3 with 451 hours was found with a stuck IP and a broken bowtie clip in the IP. I took it all apart and rebuilt if after getting parts from AMBAC ( call them the nice lady took more than 1/2 off the price compared to their online catalog and it was a A+ experience). So I put the IP back in and time it 180 deg out, curse a bit and then reinstall it with the correct timing and it starts right up and runs like a top. On a side note the fuel tank had built up crud as well as the fuel system so the tank was cleaned and the usual system flush and filter exchange. The fuel line on both units #3 & #4 from the check valve to the IP were shot and basically was just the spring to I made up a new one from soft copper and flared the ends.
Now onto the real problems for #3, the unit does not make power. I spent all weekend working on the unit tracing everything, manually flashing fields and trouble shooting the unit with some success and some failure and here is what I found. Right off the bat the speed switch was off as it pulled the starter in constantly so that was fixed in order to manually flash the field. Once running the manual field flash going back to start did nothing so I started to look at why and tried applying 12V to TB5-6? iirc, its listed in the tm, and had no success. Went onto looing at the diodes and I found that one diode had the solder joint fail, reattached it and retried the 12V to the point. SUCCESS, we were making power as long as I had 12V energizing that connection for the field. As I kept digging, I found that the rectifier bridge A4 was giving me a problem on for the field flashing and when I would ring it out it was ringing on almost every terminal which I verified in the good unit that it should not be. Took the board off and low and behold a solder bridge failed and melted, installed new jumper wires and verified that the components to what I believe are ok and put it back in the unit. I know the voltage regulator is fine since I took it out and put it in my running unit and had zero issues. Now I go to start the thing and the + line from my slave cable that is loose decided it wanted to go to ground so it wiped out my DC side. My real question is that the unit will try to start and will run but the fuel pumps will not. The glow plug relays pull in, dash lights work, start solenoid all work but the fuel pumps do not come on line I will mention that the DC breaker on the dash did not trip and is operating as normal. I disconnected the power supply to the fuel pumps and rung the wire out and am finding that it goes to ground before going to the pump. Any one have any ideas where to look before I ring every wire out?
2) DC circuit is shorting out before powering the pumps but the unit will try to start it just is not getting fuel. The unit also when it ran after being shorted, had the voltage meter indicating overcharging at one time and ran normal the other time with the fuel pumps working.
Unit #4 had the same IP issue so it was removed and rebuilt but when it was put back in it would not start up. I was getting fuel up to the injectors but it does not look like the fuel was going through the injectors into the engine. To me it looks like the injectors either were to popping or the pump was not developing enough pressure. I had all of the injectors apart on the two units and cleaned them up with the exception of the actual spring in the injector as I cannot figure out how to get it apart the cap comes off but does not bring the body with it to get down to the springs. I wonder if crud and algea got into the injectors.
3) injectors will not pop, either the pump is not making full pressure or the injectors are gummed at the springs
On a side note, units #3 and #4 o the fuel side were terrible!! Algea had taken over and I had deposits everywhere in the fuel system. Brake cleaner was needed to clean the IP's and get the parts to even move. Both of the on/off slides in the IP were seized due to being gummed up and luckily did not break any other components other than the bow tie. If you have diesel that sits, make sure you treat it. I always treat my fuel for bacteria as well as lubrication with this ULSD being rougher on older equipment but lets not talk about that debate.
Any help on these questions would be wonderful