Hello all, FNG here. I am trying to figure out how to hook up my newly acquired MEP 002a's to my house and am stumped on the cable sizing question. I have decided to use the SOOW type and am trying to figure out the gauge. I see many recommendations to use 10/4.
If I understand this correclty, 5000 watt genny, .8 PF, yields 26 amps. for each 120v Section: ((5000/./2)/120=26 amps per wire. At a 50' run of it, the voltage drop will be just under 3% (however, I believe I should be able to make this up with adjusting the voltage on the generator).
However, after going through the NEC 2008, Table 400.5 says for 10/4, with three conductors (unfortunately the neutral counts towards this) at 30 degrees C ambient , ampacity is 25 amps.
Now, that being said, will my neutral really be carrying that much current? I doubt it, especially if the panel is properly load distributed. Also, what are the chances I will be running my generator at maximum capacity with a PF of 1...
I should probably just shut up and drink the cool-aid and just use what everyone else is using. I apologize if my math is wrong (math in public, .doh) or if my logic is whacked. I read through everything I could find and just think I need someone double checking my work.
Thanks in Advance!
If I understand this correclty, 5000 watt genny, .8 PF, yields 26 amps. for each 120v Section: ((5000/./2)/120=26 amps per wire. At a 50' run of it, the voltage drop will be just under 3% (however, I believe I should be able to make this up with adjusting the voltage on the generator).
However, after going through the NEC 2008, Table 400.5 says for 10/4, with three conductors (unfortunately the neutral counts towards this) at 30 degrees C ambient , ampacity is 25 amps.
Now, that being said, will my neutral really be carrying that much current? I doubt it, especially if the panel is properly load distributed. Also, what are the chances I will be running my generator at maximum capacity with a PF of 1...
I should probably just shut up and drink the cool-aid and just use what everyone else is using. I apologize if my math is wrong (math in public, .doh) or if my logic is whacked. I read through everything I could find and just think I need someone double checking my work.