MEP-003a AC voltmeter Frequency meter Digital replacement?
Rocketman007
Kannapolis NC
My AC voltmeter 72-5008 on my MEP-003a has gone south and was looking for a replacement, however most online vendors want $$ for an exact replacement.
I saw a Video on YouTube done by Dan Walton which shows that he replaced meters with a GV25 digital meter, but no where do I see how to wire one up?
It appears that the original AC voltmeter was not monitoring the full AC output as I was not able to read the full AC output with my digital meter on the back of the bad voltmeter.
Any help to wire up a modification to replace the AC voltmeter and frequency meter would be appreciated.
JK Parker
Scoobyshep
2,312
Florida
It should be line voltage. the Voltmeter (M5) is powered from generator output through switch S8 See TM 5-6115-585-12 page 53 for the diagram. if you dont have the TMs look up on the website header click the TM button and look for the post on mep003.
Heres a very distinct possibility, you have the reconnection switch (S6) set for single phase and the meter select switch (S8 is in a 3 phase position (this happens to the best of us)
make sure the switches are set right (S8 has 1 and 3 phase marks on the label ring) run the set, make sure the main breaker is closed and verify lug voltage, then check voltage at the meter (M5)
Guyfang
27,308
Burgkunstadt, Germany
What do you mean by "Full AC output"? All three phases?
G744
4,152
Hidden Valley, Az
I'm thinking those gensets aren't quite stable enough, frequency-wise, to use a digital meter for that function without making one crazy trying to read it.
It would flicker all over the place and drive me crazy.
There is something to be said for analog instruments and humans.
Evvy Fesler
772
Roxboro, North Carolina USA
I suppose that would depend on the quality of the digital meter, it's sampling rate and so forth. Sounds like $$$ to me.
Ray70
7,181
West greenwich/RI
Actually I've used several CHEAP digital meters in the past and they were fine. I used the cheap "Domestic" rectangular digital meters with the red display ( $15 ) ( Sold domestically, but probably built in China ) as well as the rectangular ones with the blue display ( $10 ) both functioned great and were perfectly stable on both VAC and Hz, only issue was the need to make an interface plate to go from round to rectangular.
Also used the super cheap Chinese round analog gages that will fit right in place ( Hz does not need any transducer ) but they are plastic and look very cheesy and most likely won't last.
Evvy Fesler
772
Piqued my curiosity! Something like this? It can handle the input voltage range assuming it’s greater than 85v, but I didn’t see hole dimension. I was too lazy download the PDF.
Click here!
Scoobyshep
2,312
Florida
I had to replace the frequency meter on my 003 and because I think they are cool looking and I was unsupervised it got a reed style meter