MEP 005A
sparky69
Pennsylvania
Have the above generator, it stopped producing electric. Checked the static exciter, diodes on the internal board had some white crumbly powder on then. I replaced the board. with a new board. Now i have over voltage. At an idle i have 43HZ as i increase the throttle to get to 60 HZ the voltage goes high enough to trip the over voltage relay. I checked voltage and HZ with a reliable volt meter. Thanks for any help.
peapvp
1,156
Basehor, KS
Check the voltage rheostat on the front panel - if this rheostat goes out it will over excite.
Peter
Guyfang
23,410
Burgkunstadt, Germany
NEVER, EVER, Not even a bit, Idle these sets.
Guyfang
23,410
Well, that tells me you have not downloaded the TM's. Red is for the 005A.
6110-00-363-3973 REGULATOR ASSEMBLY CLA,CLB
72-2616 30554 CZN,CZM
30554-72-2616 36024
6110-00-363-3974 REGULATOR ASSEMBLY CLC,DGG
72-2611 30554