Hello Everyone,

My farming buddy got us into a project we need some advice on. He purchased a MEP 006A the other month relatively cheap but with a very low voltage output. We have looked at A LOT Of material on this site (and the manual) and I finally signed up. I will keep it brief as I am known to talk too much, but below is a list of things we have tried from the manual and various posts. I can provide further detail and pictures if need be, it’s sitting back by my old barn.

The motor runs good, we don’t have a tach, which is unfortunate. When we rev it up to about what I’m guessing is a bit under 2000 RPM (just form sound). At the courtesy outlet plugs I get 10V AC.

I measured Voltage between T1 → T2 T1 → T3 T2 → T3 Those readings all said 20v AC. Between T1 → T10,T11,T12 it was around 11 volts, The same for the rest.


























What we have done with the voltage regulator →

Replaced the voltage regulator board and transformer with new old stock from eBay. I originally ran the test using the Variac and DC Power supply. I was seeing next to no voltage on the 100ohm 25watt resistor I put on lines S and T. That is why we went ahead and got a new regulator board. After installing that board I did get volage that did drop to almost zero when I increased the AC towards 90. It was not what the manual said it would be, it was about 16V not the 25 or 30 that the manual wanted. Concerning still.

I also ran the test on the Electronic Assembly board, ended up frying the full wave diodes on that but I have replaced them since. I also replaced SCR (Q205).. The RFI module looks to have been replaced at some point, it tested out correctly. I tested the rectifier in the assembly and they all had a normal forward bias of around 0.5V. The large resistors also tested out to their specifications.

We decided just to give it a shot and re-installed the exciter assembly. Still outputs low voltage.

Rectifier Diodes on the Exciter back of Generator →

I tested all of these with a forward-biased test, they all read about 0.43V in one direction and 0L in the other. There was one I was kinda unsure about it flashed the wrong direction on the meter once.

I also attempted to test these according to the manual which references the alternator diode testing and says I should be getting less than 20 Ohms in one direction. I tried this on the back diodes (3 only so far I quit for the night last night). I’m not getting any small ohms resistance. I don’t know if its my meter or Im doing it wrong. I have the diodes unbolted and I'm checking across them. The ohm’s are in the mega ohms and one of the diodes has a measurement in both directions…

Im not sure if Im doing something wrong or not. I am not a professional electrical guy. I know enough to be dangerous. But I worry that I have not approached something correctly….

Another note: We tried to bypass K5 and flash the field if that matters, relay seems to click and we believe the speed switch is working. NOT 100% will not lie but we did try and poke at that. There are some components on the bottom of that board (part of the overload circuit?) that look like they got pretty damn hot. I don't have a picture, but the back of the board behind that big resistor is browned.














Testing at TB16 Terminals 15 and 16


This test we did last night, and at this point, is kinda why I'm reaching out for help. I hooked up the test setup as mentioned in the instructions. Started the generator, brought it up to what I think is around 1800 RPM (and then increased it anyways). Then brought the DC power supply slowly up, I went up to 24V. It looks like it should only need 4? Regardless, I never got any current draw when the ammeter, power supply, and terminals 15 and 16 were connected in a circuit. They said I could use either terminal so I only hooked it up in one direction. Dont know if that matters…. I am assuming those two lines feed into the exciter? And those are normally connected to the output of the excite assembly/voltage regulator? II tested voltage between the other terminals connected to 15 and 16 on TB16, and I didn't get anything either. The lines going into the generator (excite lines?) I measured 3 ohms.

Im really just wondering where I might have gone wrong or where to go next if anyone has any advice. I hope I dove deep enough here to provide good information I was trying to before I posted for any help.
 

Brandon314159

Member
41
3
8
Location
Portland, OR
Do you have your test rig wired up like this?

15 and 16 being the F2 and F1 terminals going into the main alternator.

Have you confirmed the fuse is good in the meter?

1751928555730.png


Also hey from just up the road from you. I was down in Lebanon last week working.
 

jasher33

New member
6
5
3
Location
Lebanon, OR
Do you have your test rig wired up like this?

15 and 16 being the F2 and F1 terminals going into the main alternator.

Have you confirmed the fuse is good in the meter?

View attachment 950003


Also hey from just up the road from you. I was down in Lebanon last week working.
I will double-check I have a feeling I might have been backwards. Ill be out side later this evening a retest that.
My friend did say he would be willing to pay for help on this if needed, if you might be interested. Ill have to talk to him first but he'd really like this working for sure lol.
 

Brandon314159

Member
41
3
8
Location
Portland, OR
There's a lot of skilled folks here so I'm sure we'll figure it out.

I'm fighting an issue on my MEP006 where my field current is higher than it should be. I'll be posting that separately but happy to help here as much as I can.
 

jasher33

New member
6
5
3
Location
Lebanon, OR
Good Morning,

I re-wired the test to TB16 terminals 15 and 16 like you drew up in your picture. I'm still getting the same results, its not pulling any current at all. Not voltage change on genertator.

Does this indicate I should be looking harder at the rectifiers on the exciter? I had that fishy one, or should I go deeper into the generator itself? I don't have the proper equipment mentioned in the manual to test the winding accurately. Though I can figure something out if need be.

Thanks for any help; I appreciate it a lot. I'd love to see this old unit breathe life. (Well, I'll get it; I'm too stubborn to give up ;)
 

Brandon314159

Member
41
3
8
Location
Portland, OR
You mentioned that you measured 3ohms across 15 + 16 headed to the alternator?

If so, you should be drawing some current when you apply the lab power supply. Perhaps you have a bad lead or the meter fuse it blown? Can you post a photo of your setup?
 

jasher33

New member
6
5
3
Location
Lebanon, OR
Well, thank you, Brandon,

Made me realize that there had to be something wrong with my test setup because it would draw current anyways! Yikes, well here are my new results. It seems like I'm making partial power now. I don't have a tach as I mentioned so I didn't throttle it all the way out in this test but reved it up to till it seemed reasonable.

I switched meters and figured out there was a setting on my power supply that I didn't realize, and it just flat wasn't working right.

Now I am getting the current draw, it seems like it matches the book. At about 4 volts its around 1.4 AMPs, I put it up to five and it sat at 1.7 amps.

At the courtesy plug at the max I revered it to (I left the supply at 5v 1.7A across those two terminals (TB16 T15 and T16), Im now getting 66V AC.

At the terminal block between T1, T2, T3 those are all reading around 120V AC.
T1 -> T12 and such was 66 V AC

My output plug is just not getting voltage yet but Im assuming thats another problem.20250706_202409.jpg

Is this set correctly for higher voltage?

Im curious how to proceed now, I didn't want to go to further with anything without an opinion. Here are a couple shots if they provide anything else useful.
20250708_114344.jpg
 

Brandon314159

Member
41
3
8
Location
Portland, OR
Yay for progress.

That voltage select 'card' is set for 120/208 WYE currently. If you move it up one, you'll get 240/416 WYE (not delta).

The way it is currently, at 1800RPM/60hz you should be getting 120V between T1 and neutral with everything set correctly. You can check output HZ with the gauge on the front panel. You'll see 60hz indicated when you're at 1800RPM

What are you wanting to power with this generator?
 

jasher33

New member
6
5
3
Location
Lebanon, OR
Yay for progress.

That voltage select 'card' is set for 120/208 WYE currently. If you move it up one, you'll get 240/416 WYE (not delta).

The way it is currently, at 1800RPM/60hz you should be getting 120V between T1 and neutral with everything set correctly. You can check output HZ with the gauge on the front panel. You'll see 60hz indicated when you're at 1800RPM

What are you wanting to power with this generator?
Ok I will poke around more tonight after work, Im assumming my exiter assembly is bonked like I thought if this end up working.

We are going to power a seed cleaning system. We are restoring an old seed cleaning machine from the 40s (29D I believe). It has an old Fairbanks Morse 5ph motor that setup for 220, I got that old beast cleaned up and working. We have another seed cleaner with an old 3 phase motor we want to get working. Then with the entire setup, there will be a few more electric motors to power various parts of the system.
 

Guyfang

Moderator
Staff member
Moderator
18,088
27,147
113
Location
Burgkunstadt, Germany
Should you have doubts about the A5 card, Member @kloppk makes and sells a brand new replacement. The A5 card is a known "problem" part, and they aint getting any younger.

Initial excitation comes from the S9. So with or without the Static Exciter, you can apply 24 volts at F1 & F2 to light off the main gen, for test purposes. From the pictures, it looks like the main gen is toast. But it remains a question mark until you properly test it.
 

jasher33

New member
6
5
3
Location
Lebanon, OR
Thank you very much every body!

I will be taking my kids camping for the next frew days up in the mountains. Ill be getting back to fiddling with this next week. I appreciate the guidance very much.

@Guyfang
If we figure out if the main generator is good enough we might be looking at getting that board. So thanks for the tip there!

I'm going to take a hard look next week at this wiring. I found traces of people trying to figure out this low voltage already, of course. Plus It looks like the wiring has been fused with a bit. I see what looks to be new connecting ends. I mean its been around for years Im sure many hands have been in it.

For fun here are afew more pics. One of that back of that terminal block and that relay board.


6849481366044488522.jpg8688044237548971786.jpg8090537588877501518.jpg
 

Guyfang

Moderator
Staff member
Moderator
18,088
27,147
113
Location
Burgkunstadt, Germany
View attachment 950140
A5 card dosn't look bad. test it, its simple. go to the -34 TM and the procedure is there.


1752083080474.jpeg

I personally, would remove every wire on TB1. Then using the wire schematic, replace them taking my time. If someone at an earlier point in time fooled with TB1 and get 1-2 wire on here wrong, the only way to find it without committing suicide, is to just start from scratch.


Do not forget to look at both sides of the two cards in the Static Exciter. See if they are burnt or traces burned off.

Enjoy the camping! I have my Grand Kids camping out in my living room, tent and all, right now. I simply love it!
 

Brandon314159

Member
41
3
8
Location
Portland, OR
I will upload a photo of the back of my TB1, it's known good operational. I pulled all the 12 lead wires off so I could pull the bell apart and do testing, but I left all the small ring terminals in place where they go. You wiring, other than missing some wrap that likely degraded and fell off, looks like mine.

The metal tags on the larger leads should be in order T1-T12, from what I can see it looks correct but you'd want to check each one.