mep-017a let me down

powerwagon

New member
21
1
0
Location
northeast pa
let me first say i am no electrical wiz. during the last storm i started my generator and ran fine, here is the trouble. powered the house up still ok for a short time, then no power gen is still running fine. tried the flash no help checked fuses all checked ok, but no power to the fuse holders or gen plug. i just checked the flash switch it's ok i have 24v there. i think its the vr? i have the old hockey puck style what wires are the 2 field wires that i need to apply 12v to? this has always worked fine until now. if the vr is bad what can i put in it's place? does flight systems sell a replacement since the usgi one are like hens teeth.
 

powerwagon

New member
21
1
0
Location
northeast pa
update, i applied 12v to 5&6 wires at the vr and i get no power, i hooked up wires 5&6 to regulator and ran gen hit the flash switch and got 24v at field wires at vr? now what..
 

jbk

Member
404
5
16
Location
livingston la.
the new style reg. are still out their. call jay at satutn surplus. i paid $125.00 for a tested used from them. with the new style reg. you have to change out that vaiable voltage pot on the control panel. i havnt used any of thr aftermarket reg. maybe somone here or at smoke stack has.
 