MEP 1030A

peapvp

Well-known member
Steel Soldiers Supporter
1,311
1,688
113
Location
Basehor, KS
Robert,

It sounds like it to me that you are a newbie if it comes to multimeters.

We usually recommend this multimeter tutorial made by an unaffiliated
Company

 

LuckeyD

Well-known member
148
429
63
Location
Vilseck, Germany
Good Day: Just bare with me here. On that J2/P2 there are pins DEF and def. DEF are on the outer ring of the connector and DE go to nothing(similar to your strange readings), and F goes to the K1 main contactor, pin X(also similar to your test readings). def on the other hand are located on the inner most portion of the P2 connector and they all 3 traves down to the relay box to connector P5B/J5B gray connector and inside the box they connect to P11/J11 connector pin 1 and from there it goes to the starter motor where a bunch of wires connect to the one stud of the starter mounting bolts forming the B- chassis ground. This is all on FO1 sheet 3 of 6. I'm a bit slow at my age so I stuck the nose into the foldouts.

For your meter, set it on reading resistance and put the leads together, if set to make noise this is what your looking for, 0 resistance and making a noise if you set it on that position. Easily checked if you place one lead on d,(inner most pin on J2) to that ground braid that is supposed to be connected to the DCS. Or any good chassis ground. Should get no resistance, straight shot, chassis ground. Now, if all is in order, you have B+ and B- to the DCS and it should power on.

If not, best to take it inside to a well lit table and start looking inside that very clean DCS as it is not working and hopefully find an issue inside the DCS and they never published anything on the inside of the DCS where things go like a schematic as it was proprietary as they said. Yes, I asked in 2009. There are on circuit board circuit fuses. If everything is NOT in order, check that P11/J11 connection that you have good connection from the J2/P2 pins def to that J11 pin 1, (if no connection time to open the box and see why not)and then if good from the P11 to the starter stud. I hope some very intelligent person changed the starter (common issue) and missed a wire and all will be in order once put back in place.
 
Last edited by a moderator:

Robert P

New member
15
6
3
Location
Ca
Hello. UPDATE.. so with all the help ive received i made progress, the Panel is active and the generator starts and sounds great, ive have been able to correct 3 faults that prevented starting, now what i believe to be the last fault is this Excitation fault, I believe it has lost its magnetism and cant find the location of the the 2 wires to apply 12v to briefly to correct this issue, if I recall f1&f2, it shows the wires located inside the panel and i cant find them and believe them to be located elsewhere, or the ACpower head is bad, this generator has well under 1000hrs so im hoping its thw prior mentioned issue. Any thoughts would be truly appreciated.
Robert
 

Robert P

New member
15
6
3
Location
Ca
Good Day: Just bare with me here. On that J2/P2 there are pins DEF and def. DEF are on the outer ring of the connector and DE go to nothing(similar to your strange readings), and F goes to the K1 main contactor, pin X(also similar to your test readings). def on the other hand are located on the inner most portion of the P2 connector and they all 3 traves down to the relay box to connector P5B/J5B gray connector and inside the box they connect to P11/J11 connector pin 1 and from there it goes to the starter motor where a bunch of wires connect to the one stud of the starter mounting bolts forming the B- chassis ground. This is all on FO1 sheet 3 of 6. I'm a bit slow at my age so I stuck the nose into the foldouts.

For your meter, set it on reading resistance and put the leads together, if set to make noise this is what your looking for, 0 resistance and making a noise if you set it on that position. Easily checked if you place one lead on d,(inner most pin on J2) to that ground braid that is supposed to be connected to the DCS. Or any good chassis ground. Should get no resistance, straight shot, chassis ground. Now, if all is in order, you have B+ and B- to the DCS and it should power on.

If not, best to take it inside to a well lit table and start looking inside that very clean DCS as it is not working and hopefully find an issue inside the DCS and they never published anything on the inside of the DCS where things go like a schematic as it was proprietary as they said. Yes, I asked in 2009. There are on circuit board circuit fuses. If everything is NOT in order, check that P11/J11 connection that you have good connection from the J2/P2 pins def to that J11 pin 1, (if no connection time to open the box and see why not)and then if good from the P11 to the starter stud. I hope some very intelligent person changed the starter (common issue) and missed a wire and all will be in order once put back in place.
 

Attachments

Robert P

New member
15
6
3
Location
Ca
Yes, everything i could find to test, tested good and found no issues with the wiring, connectors fuses, relays, it was those kind of issues that i was able to clear to get to this point. Im lost at this point and believe it must be the DCS panel or AC powerhead.
 

kloppk

Well-known member
Steel Soldiers Supporter
2,341
4,234
113
Location
Massachusetts
Have you tested the Exciter Stator resistance to be sure it's good? TM says it should be about 12 ohms.

Have you measured the DC voltage going to the Exciter Stator while the genset is flashing the gen head to verify the DCS is sending the flashing voltage?

If you do see a flashing voltage to the field then check to see if there is voltage at that time at the convenience outlet to see if the Exciter Rotor, rotating diodes and stator are working.
 

Robert P

New member
15
6
3
Location
Ca
I did check the convenience outlet and the meter didn't show any signs of voltage, ive began taking things apart to get better access to the exciter stator and will check it soon for both 12 ohms and voltage. I would be looking for 12v not 24v going to the Exciter correct? I'll do some research when I have time this week.
Thanks
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!