• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP-1040 Fault 2335 "Excitation Fault"

peapvp

Well-known member
Steel Soldiers Supporter
1,281
1,633
113
Location
Basehor, KS
Check wiring from A1 P1 J K to P90 J90 1; 2 to F1 and F2
Connect DC meter and on J90 1; 2
start Genset
at 600 rpm watch DC Meter on J90
If there is no DC then A1 needs to be repaired.
A1 contains exciter / AVR

Peter
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
4,037
6,754
113
Location
MA
This item is not in my possession. Available semi-locally and the guy is asking way too much for its current non generating 'paperweight' state. Was doing some preliminary investigating.
 