• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Mep 531 breaker tripping as soon as engine starts.

GASCANS001

Member
38
48
18
Location
Fairmont West Virginia
I’m working on a 531 with no power. The breaker is also tripping once it starts.
The frequency and voltage gauges both work and show correct values.

I have 120 at the gauge and 120 on the back of breaker labeled “a+ and a-“ I think that’s the right label. Pretty sure my readings are on the “supply” side of the breaker. I’m not sure where the load terminals are so I can’t test for continuity from the load terminals to the other terminals for a broke wire that’s grounding out. The top and bottom most wires on the back of the breaker is what I tested for voltage and I that’s where I got the 120v. The center two wires I have no idea where they go or what they’re for. Dug through the whole manual and couldn’t see anything coming clear.

I checked continuity between a bunch of different connectors relating to 120v . All were OL good.
The one that showed resistance was the 24v supply from the slave POS & the L terminal on the back of the load terminal block.

not real sure where to go from here.
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,079
113
Location
Burgkunstadt, Germany
Sometimes pictures are a very good idea.

What Breaker? Calling by the Military nomenclature helps keep everyone on the same page. All parts have something printed next to them with what it is. A circuit breaker would be for instance CB1 or CB3.

If you don't know where the load terminals are, you need to spend a little time with the TM 9-6115-639-13&P
 

GASCANS001

Member
38
48
18
Location
Fairmont West Virginia
Sometimes pictures are a very good idea.

What Breaker? Calling by the Military nomenclature helps keep everyone on the same page. All parts have something printed next to them with what it is. A circuit breaker would be for instance CB1 or CB3.

If you don't know where the load terminals are, you need to spend a little time with the TM 9-6115-639-13&P
I just was out playing some more.

everything tested good for continuity. (No broken wires.)

with the unit off, load circuit breaker (CB1), I have a reading from load to supply power on the load circuit breaker (CB1).

I went over the manual multiple times. I’m just as confused as I started.

I ran the set and tested the dc output for the hour meter and was getting 45v DC.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks