- 753
- 1,332
- 93
- Highland, Indiana
Have a Mep 802A that has power to receptacles. Only power to lugs when I hold up the contact switch. As soon as I let go the light goes off and no more power to lugs. K1 was replaced. Any suggestions?
Thank you!So I believe he means he is able to "close" the contactor by holding the switch, but it doesn't stay closed.
"Trip" was probably not the best term to use...
Did you check the switch to ensure the diode is installed ( correctly ) and you should also verify the diode is good.
If that all checks out, you may have a bad overload relay, the black box all the way to the left inside the control panel, behind the outlet.
The signal to close K1 runs through the overload. I once had a unit doing the exact same thing and the overload was faulty.
However, you have to verify the switch and diode are good per Kurt's reply #2 , before moving on.
Start with the easy things first, then move forward...
The light comes on if I hold s7 up. And there is power to lugs.And no idiot light comes on?
Oh boy. Let me flip this around.The diode is installed backwards!
The stripe should be on the RIGHT. Like this...
I owe you a steak dinner! Thank you so much!The diode is installed backwards!
Check to see if there is a diode across S5 terminals 2 & 5. Verify end of diode with the stripe on it is connected to terminal 2.
That's why it's very important to read everything and check everything carefully.
If you hadn't posted that picture we would all have assumed you verified both the diode's correct orientation and functionality and moved on to the next idea!
Luckily Kurt has a keen eye!
Glad you got it fixed for Zero$
.And that little change could have been the reason why this machine left the pool.... funny, right?