Got my 802A running today
I plugged in a 1,000 watt heater into the outlet and within a couple of seconds the heater stopped.
No power at the outlet.
According to the schematic CB3 controls the power to the out. I looked all around the control box and no CB3 to be found.
What I did find was a black in-line fuze holder to the left of the relay block cable tied to the wire harness. The 9 amp fuse in it was blown. Put a new one in and power was restored to the outlet.
Do others have the in-line fuze holder or a real CB3?
Where is CB3 suppose to be located?
Here is a picture of the fuse holder.