Got a new (to me) MEP-802a that looks like it was in mid-rebuild and they threw in the towel, but I'm making progress and now need some advice on the output contactor (K1).
Some background:
So now K1 will close if I move S5 to Closed, but when I release the switch it opens again. So I'm sure if it's K1 or S5 that's not working correctly.
Any thoughts?
Some background:
- Picked it up with 75% of the panels having a couple of screws holding them down.
- Looks like a new (2010 rebuilt) motor.
- Had a destroyed starter solenoid, looks like someone screwdriver jumpered the wrong two terminals to test it. (replaced)
- The K2 relay is intermittent in working, and the K18 relay had all it's wires loosely attached.
- The P6 harness looks brand new.
- Found all the small wires on K1 were installed in the wrong locations. (X,Y,11,12)
- When powered on, K1 was always engaged with no way to shut it off.
So now K1 will close if I move S5 to Closed, but when I release the switch it opens again. So I'm sure if it's K1 or S5 that's not working correctly.
Any thoughts?