MEP-802a Power Quality (With oscilloscope pics)

Digger556

Well-known member
Steel Soldiers Supporter
330
829
93
Location
Denver CO
Most folks know the MEP units with brushless genheads make clean power. However, I've always wondered how clean.

I used a Rigol DS1054Z scope with a Micsig differential probe to do the measuring and screen captures. (So I don't blow up the scope)
ds1054z-front-1200x735-White-b.jpg


For baseline reference, here is incoming power to the house. Pretty clean with slight clipping at the peaks.
48733769572_0e714c6abe_o.jpg


MEP-802a: The 802 was loaded to 3kW pure resistive load. The waveform is pretty clean with some "peakyness". All in all not bad.
48733769427_2128fe816b_o.jpg



For comparison, a Honda EU2000i inverter generator:
48733257448_427eb1a341_o.jpg



A Xantrex ProSine 2000 inverter:
48733769082_59bbecaa89_o.jpg


A Xantrex ProWatt 600 inverter (this is a cheap pure sine wave inverter):
48733256658_88e5c9482d_o.jpg


And finally a Vector MAXX 700 watt modified sine wave inverter:
48733256988_8063923b51_o.jpg



Overall I would award highest quality output to the Xantrex ProSine 2000. It has a heavy surge capacity (4500watts) and it reacted quickly to the load changes without distorting the output. 2nd would go to the Honda EU2000i. Its steady state output matched the ProSine, but had some clipping when big loads were applied. You can't really fault the generator too much, the mechanics of the engine just can't react as fast.

The MEP-802a came in 3rd. Not quite as good as the first 2, but still good or better than line power is some cases. This is really splitting hairs at this point. The practical reality is the 802a is just as good as line power, the Honda or the ProSine.

The Xantrex ProWatt 600 was about 1/10th the price of the ProSine and it shows in the output. The distortion remained regardless of load. It's not terrible, but could be better.

The Vector 700 is clearly the worst of the group, but I threw it in for comparison. Actually for a cheap box store inverter, its output holds very steady and is only limited by the nature of it being a modified sine wave design.
 

Chrispyny

Member
294
13
18
Location
NY
Excellent. By chance can you show what a couple open frame ‘noise, smoke and fume’ generators look like if you have any to test? To give our viewers a baseline and to show why we are such big fans of the mep-802/803 gensets please?
 
Last edited:

Digger556

Well-known member
Steel Soldiers Supporter
330
829
93
Location
Denver CO
Yes, I don't have one, but I'm tracking one down. I also have a friend with a 3500watt Predator Inverter generator.


Here is a screen shot from a YouTuber testing a Coleman 5000 watt open frame, 3600 rpm generator.
Noise and fume.jpg

https://youtu.be/QNo1mUCpQnI?t=22
 
Last edited:
Top